Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Navien NCB 210 CONDENSATE
Bill Julian
Member Posts: 162
in Gas Heating
Installed many of these but now I have no place to run the condensate line. The plumbing is not assessable. I did one years ago where i went outside with the condensate tube.
My issues is freezing. Anybody have experience wit this? If I do go outside how can it be done to prevent freezing here in the northeast?
My issues is freezing. Anybody have experience wit this? If I do go outside how can it be done to prevent freezing here in the northeast?
0
Comments
-
Have the condensate from the boiler drain into a laundry sink pump like a Liberty 404 and plumb the discharge with 11/2” like a sump pump.0
-
Thanks I found a plumbing source. I cut in a trap0
Categories
- All Categories
- 85.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 78 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 94 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 59 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 377 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements