Heating all zones at once or make them take turns?
amSteve
amSteve Member Posts: 2
Consider a residence with a manifold supporting 6 zones/pex loops that, taken together heat 1600 sf. It's an open floor plan without walls between entry/living/media/dining/kitchen. Beds and baths are on a different manifold.
Floating slab on grade -- 2" formular on the grade -- 1/2" pex stabled to the formular, covered by 4" inches of concrete.
Is it more efficient to run all zones wide open at once or can an argument be made that it's preferrable to devote the full boiler output to one zone at a time.
thx!
    hot_rod Member Posts: 27,819
    In a perfect system you would like to match the heat input to the heat loss without a lot of stop and starting of the components, boiler, pumps, valves, etc.
    The most efficient mode to run the boiler is off :)
    Next best is in it's "sweet spot" if it is a mod con, the lowest possible return with the burner modulating around the ever changing load, no, or very few stop/ starts.
    A properly sized and installed mod con on reset control, zoned within its modulation is about as good as it gets. If micro zoned below the lowest turndown, most mod cons are, in shoulder seasons especially, a buffer can help eliminate cycling.
    It always comes down to how good is good enough, control and $$ wise.
    Alan (California Radiant) Forbes Member Posts: 4,803
    edited March 2021
    If bedrooms aren't involved, I like one zone, especially if it's an open floor plan.
    Canucker
  • amSteve
    thx -- appreciated.