Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

tekmar 374 mix 1 open error

Options
Hi,
Old heating guy new question.
My tekmar seems to have a messed up mix 1 circuit and will not display the percentage graph on the display.
I moved the sensor and demand to the unused mix 2 but now I have an open error on the mix 1 and cannot seem to get it turned off. Beside what I have done anybody have some fresh info?
Thanks

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited February 2021
    Options
    Open error on Mix 1 means it can’t read the sensor, which you removed. It’s possible the sensor is bad. Did you check that first?
    Is there any wire connected to terminal 25?

    There was an error rendering this rich post.