tekmar 374 mix 1 open error
dougbigfoot
Member Posts: 3
Hi,
Old heating guy new question.
My tekmar seems to have a messed up mix 1 circuit and will not display the percentage graph on the display.
I moved the sensor and demand to the unused mix 2 but now I have an open error on the mix 1 and cannot seem to get it turned off. Beside what I have done anybody have some fresh info?
Thanks
Old heating guy new question.
My tekmar seems to have a messed up mix 1 circuit and will not display the percentage graph on the display.
I moved the sensor and demand to the unused mix 2 but now I have an open error on the mix 1 and cannot seem to get it turned off. Beside what I have done anybody have some fresh info?
Thanks
0
Comments
-
Open error on Mix 1 means it can’t read the sensor, which you removed. It’s possible the sensor is bad. Did you check that first?
Is there any wire connected to terminal 25?There was an error rendering this rich post.
0