LWCO V9 nipple heights

JPomp
JPomp Member Posts: 1
Hello all!

Was curious if any one had information pointing to the nipple lengths for a 150 control on a Burnham V9. I searched Burnhams directions and only found the required heights for proper operation. Not the length of the nipples to get me those heights.

Thanks for any help,
Jamie

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 2,973
    The Hartford loop hight on the equalizer , the lower part of the tee where the return pipes though a short nipple needs to be set at he minimum water line on the boiler ... From there you need to use a tape measure ....

    There was an error rendering this rich post.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,248
    @JPomp

    You could probably call Burnham and ask. But most people if they know the correct height figure it out with a tape measure. 1" nipples make in about 5/8"