Rezoning: Multiple manifolds one zone?
Zone 1: 300 sq ft: master bedroom, bathroom and closet.
Zone 2: 1200 sq ft: 2 bedrooms, bathroom, living room
Zone 3: 300 sq ft: kitchen, dining room, and laundry
My first issue is that my manifolds don't have flow meters and it turns out I was flowing water too fast through the mixing valve and got terrible groaning noises from the boiler as a result. I turned them down an unknown amount, but obviously need to know what they're flowing. Has anyone used the RHT flow meters? Any thoughts?
Second issue is that most of the whole house except the bedrooms are open, and south facing.
Zone 1 works great.
Zone 3 works great.
Zone 2 does a good job in the living room, but that often gets a lot of solar gain and the two bedrooms on the north side of the house get really cold
I was thinking of either splitting Zone 2 into two zones (it's currently 6 loops), which would require another valve on the panel and another thermostat (the taco controller can do 4 zones), or doing the split on zone 2 and combining the living room portion of zone 2 with zone 3. The reason they're not the same zone in the first place is due to the kitchen being a single step (i call it the death step because it nearly kills me daily) up from the living room. Could I put in a tee on the inlet and outlet going to two manifolds? Would I need to chain them together a different way?
Hopefully that makes sense, thanks!
Comments
-
Yeah, that's probably true. Here ya go! To reiterate the north bedrooms get cold, and I was considering either splitting zone 2 into two separate zones, or combining 2a with 3 somehow, and making zone 2b it's own zone. Thanks!
0 -
Bottom line is you need adequate flow to move the heat load. With a tankless heater you could be bottlenecked there?
You can increase radiant output by either increasing flow rate, or increasing temperature. Only so much you can squeeze out by flow increase, it starts to taper off the % of additional output for extra pump power required, and velocity noise and wear becomes a concern. see below. 2-14 is a typical 250' 1/2" loop in concrete.
Maybe try increasing the supply temperature and stay below 83F floor surface.
What type of floor covering in the bedrooms? Lots of furniture covering the floor? Two outside walls on those bedrooms makes the load a bit higher probably.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It's not that it can't get warm in those rooms, it's just that on a cold, sunny day (the main kind we have in Utah) the boiler and pump shut off because the solar gain gets the ambient temperature in 2a high enough and 2b, which gets no solar gain gets cold. Identical ceramic tile in all rooms.
As far as flow rates are concerned, I have absolutely no idea what they are because I don't have flow meters on any of my loops. When I ambiguously turned them down to another unknown value, the boiler quieted down a lot. I also turned down the output temp from 120 to 110.
I've got these manifolds: https://www.blueridgecompany.com/radiant/hydronic/807/rht-ss-hf-stainless-steel-high-flow-manifolds
and either need to replace them or add flow meters to them (which will be a pain, but...)0 -
Hi Arbakken, I have a similar system from Blue Ridge, with a boiler, manifolds, and radiators. I bought the system. I bought this system a year ago with the understanding from the company that this was easy to install by any plumber. I still haven't found a plumber in Santa Barbara who will install the boiler. The house is finished and we don't have an HVAC system working. I didn't know what boilers were unusual in Santa Barbara. I just chose it instead of a furnace to save energy. Any advice on the installation? I am not a plumber but I may have to become one to get this white elephant installed.
0 -
Yes the #2 zone needs to be split.
Even so the solar gain may over-power the south facing rooms. Really the only way to make that better is operable shades of some sort. Turn off the solar gain.
This has a common problem here in Utah where I have been doing radiant for many years. Everyone wants that free solar heat and often southern views, but never considers the solar gain with close to 300 days a year of sunshine.
It gets complicated, but on a few jobs we designed with constant circulation and could move some of the solar gain from the hot rooms back to the cold rooms.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements