Sterling GarageGuy Heater Control Board

BrennanU
Member Posts: 7
Hi All,
I have a Sterling GarageGuy series heater installed in my garage. It has been working fine for years, but last night I noticed it wasn't heating properly. During the cycle the gas shuts off and the unit stops. Error code reports a no flame condition. I was poking around with my meter and there seems to be some weird voltages going on during the problem times of the cycle. During this process the voltage going to the gas valve drops down to ~12VAC and I can hear the combustion fan clicking on and off fairly randomly, as if the relay is right around the coil voltage. I've checked the 24VAC transformer during this time and it is putting out the correct voltage.
This all leads me to believe the control board is the problem. Checking online the OEM replacement board appears to be ~$250. With some further research, I see that both Honeywell and White-Rodgers make a number of universal controllers, but I can't seem to find one that is rated for Direct Spark ignition and has full control over the blowers (combustion air and heat blower). Does anyone know if such a universal replacement board exists, or is the OEM board my only option?
The board seems to be an OEM generic board labeled 1097-507. The correct part is a 11J28-06881.
Thanks!
I have a Sterling GarageGuy series heater installed in my garage. It has been working fine for years, but last night I noticed it wasn't heating properly. During the cycle the gas shuts off and the unit stops. Error code reports a no flame condition. I was poking around with my meter and there seems to be some weird voltages going on during the problem times of the cycle. During this process the voltage going to the gas valve drops down to ~12VAC and I can hear the combustion fan clicking on and off fairly randomly, as if the relay is right around the coil voltage. I've checked the 24VAC transformer during this time and it is putting out the correct voltage.
This all leads me to believe the control board is the problem. Checking online the OEM replacement board appears to be ~$250. With some further research, I see that both Honeywell and White-Rodgers make a number of universal controllers, but I can't seem to find one that is rated for Direct Spark ignition and has full control over the blowers (combustion air and heat blower). Does anyone know if such a universal replacement board exists, or is the OEM board my only option?
The board seems to be an OEM generic board labeled 1097-507. The correct part is a 11J28-06881.
Thanks!
0
Comments
-
Not sure how I managed to post this in job opportunities, but if someone could move this to the appropriate section, that would be great.0
-
Are you getting 2 flashes on the control board?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hourTwo btu/ per sq ft for degree difference for a slab0
-
Yes, getting 2 flashes on the board. I took the flame sensor out and cleaned it up with no success. Other than being a little bit dirty, it looked fine.0
-
I had a similar problem with my heater this week. I found two cracked solder joints on the 6 pin connector; one is the wire to the gas valve. I resoldered them and all is working correctly again. Hope this helps you.
0
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 769 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements