adding a wi fi stat to an existing trolatemp forced air zoning system

i'm interested in connecting a honeywell t6 pro wi fi stat to an existing mastertrol mark 2. model mabs2-3. can't figure out how to wire it. any thoughts?

Comments

  • SuperTech
    SuperTech Member Posts: 2,401
    Basically you just can't do it. You will need to replace the zone control with something modern.  That control has one thermostat as the "master" zone. Its the only zone that can switch the system from heating to cooling. That thermostat uses both the O and B terminals to do so. The "slave" zone uses less wires. I was never a fan of this setup.  

    A new zone control board from a manufacturer such as EWC or Honeywell will allow for better,  more reliable operation of the system.  You might be able to re-use the same motorized duct dampers, but I would update those as well if possible. 
  • HVACNUT
    HVACNUT Member Posts: 6,283
    In addition to the advice from @SuperTech, make sure to use a dedicated 40va transformer to power the new zone panel.