Hello,
I am unclear about the standard of pipe I need to use for my DWV (sanitary drainage for a 2-unit) application to meet UPC 2015. TABLE 701.2 refers to Schedule 40, whereas pipe and fittings have different requirements in terms of standards. Fittings that I can buy from big box stores are marked DWV, but not marked schedule 40. Yet, they are used by plumbers and DIYers alike and seem to be the right fitting. Furthermore, they are listed as schedule 40 on some web sites, despite no marking on the fitting as such.
My interpretation is that if the fitting meets ASTM D 2665 then it meets code, and does not need to be marked schedule 40.
Whereas pipe meets ASTM D 1785 and IS marked schedule 40.
I am over-thinking here? I do want to be sure code inspection does not identify wrong fittings!
in a head spin,
Shawn
I am unclear about the standard of pipe I need to use for my DWV (sanitary drainage for a 2-unit) application to meet UPC 2015. TABLE 701.2 refers to Schedule 40, whereas pipe and fittings have different requirements in terms of standards. Fittings that I can buy from big box stores are marked DWV, but not marked schedule 40. Yet, they are used by plumbers and DIYers alike and seem to be the right fitting. Furthermore, they are listed as schedule 40 on some web sites, despite no marking on the fitting as such.
My interpretation is that if the fitting meets ASTM D 2665 then it meets code, and does not need to be marked schedule 40.
Whereas pipe meets ASTM D 1785 and IS marked schedule 40.
I am over-thinking here? I do want to be sure code inspection does not identify wrong fittings!
in a head spin,
Shawn
0
Comments
-
-
Cellular core PVC is most common for DWV. Lighter, easier to work with.
Venting some boilers requires solid core or CPVC.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:Cellular core PVC is most common for DWV. Lighter, easier to work with. Venting some boilers requires solid core or CPVC.0
-
The cellular core is also a good bit noisier for drain lines than the solid type. A bit of forward planning and work is need if you don’t want to hear “water events” throughout your house.PC7060 said:hot_rod said:Cellular core PVC is most common for DWV. Lighter, easier to work with.
Venting some boilers requires solid core or CPVC.
We used cast iron for any 3" vertical piping within a home.
The other key is to always put 3" DWV in a 6" plumbing wall. If it touches the framing or sheetrock it can be really noisy.
One inspector was adamant about seeing a labeled "transition" band used on the plastic to cast connection, not a standard no-hub band.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
“The other key is to always put 3" DWV in a 6" plumbing wall. If it touches the framing or sheetrock it can be really noisy”@hot_rod - agree, recently used the PVC horizontally in 2x6 wall and packed bay with Roxol Safe and Sound. Also put under key horizon line to quiet drain, terlet and tub especially.You can still hear the vertical drains, but about at same level as CI. Horizontal are very quiet. $100 well spent0
-
the DWV fittings at the vast majority of box stores will be sch 40. There is SDR35 which is a thin wall pipe approved for buried service lines, but not for indoor plumbing afaik. SDR35 is very thin (maybe 3/32") compared with sch 40. You will know the difference. If it is labeled DWV you should be fine.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements