Tekmar 256 Outdoor boiler reset Question

gp1976
Member Posts: 4
Hello everyone,
I was hoping someone could help answer a question for me, does the Tekmar 256 maintain a minimum boiler temp or does it cold fire the boiler, the manual doesn't say much.
Thank you in advance for any help.
I was hoping someone could help answer a question for me, does the Tekmar 256 maintain a minimum boiler temp or does it cold fire the boiler, the manual doesn't say much.
Thank you in advance for any help.
0
Comments
-
Depends, terminal #7 	 when close by a jumper or boiler demand switch will allow the boiler to fire. The outdoor air temp will determine how hot the boiler water gets.0