Honeywell aquastat L6006C for fan control - temperature settings

Hello,
I have a heating system with oil boiler and forced air. I would like to know the recommended settings for my fan control aquastat Honeywell L6006C.
The boiler aquastat (L8124A) is set to 180 Hi and 160 Lo with 10 Diff.
I want to get the most optimum heating from the fan blower aquastat (L6006C) so any recommendations will be greatly appreciated.
Thanks

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,364
    Usually you bring on the fan at about 120 and shut down when the temp is below 100 to prevent blowing cold air.