When to use valve-on delay and motor-off delay?
CLamb
Member Posts: 319
in Oil Heating
I'm looking through the manual for the Beckett AFG oil burner packaged with a Weil-McLain SGO-3. It says that the GeniSys controller has provision for valve-on delay and motor-off delay but doesn't say anything about when they should be used. Can somebody please explain?
0
Comments
-
The valve on delay can be used for any application . The valve on and motor off delay must be used for a direct vent , no chimney , vented out the wall application .
There was an error rendering this rich post.
0 -
What model GeniSys? 7505A, B, or P?
This is a late model with the Clean Cut pump? If so it should be a B or P.0 -
-
I'm pretty sure most or all oil burners in production today use valve-on delay. There's no reason not to- it makes the starts and stops a lot cleaner, and helps to reduce soot buildup. I tried valve-on delay on my own burner (Sunray FC Bantam at that time) years ago and saw the difference- now we add it to all our customers' burners that don't have it. Beckett makes a nice delay valve kit that will fit most burners.
Motor-off delay is used for direct-vent jobs as @Big Ed_4 says, also for boilers with a lot of back-pressure in their flue passages. In the latter case, the spec burner will have it enabled.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
As @STEVEusaPA said "Always" If there is a choice, use the longest off delay for direct vent applications. If you have a standard chimney vented appliance, the time can be set to the shortest off delay, or 30 seconds minimum. anything less than 30 seconds.. why bother? The idea is to reduce convection heat in the combustion chamber from heating the oil in the nozzle line and nozzle. This causes after drip, then that oil is baked and it forms a coating on the nozzle and electrodes
So use post purge always when available.
Yours truly,
Mr.Ed
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements