Hi there. This is my first post. I hope its ok. I've got a 600 sq.ft. garage with in floor heat. All insulated and I have it at 63 degrees. works great I heat it with a 4500 watt water heater. Three 200 ft loops. My pressure goes to zero ( or near zero) when it is in cycling mode. I've tried to pump it up but can only get to 15 psi. It stays there until it cycles. Goes to zero and when it stops it goes back to around 15 psi. Any thoughts? Thanks.


0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 562 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
A picture or a diagram would help
Retired HVAC Contractor from So. Jersey Shore.
Cleaned & services first oil heating system at age 16
Specialized in Oil Heat and Hydronics where the competition did Gas Warm Air
If you make an expensive repair and the same problem happens, What will you check next?
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me
Which pump setting are you on? Try speed 1 see how it changes pressure. As I see it you are pumping at the expansion tank, should be pumping away,
Was the panel built that way?
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me
Thanks again.
(I realize this is over simplified but it's illustrating my point)
Personally I would move the expansion tank, pressures will be better and air removal improved.
Or you could remove the tank, pump it to 20 psi, reinstall and pressurize the system to 20 psi, then you may see 5 psi or more at the gauge when it is running.
Not sure if you are looking for a work around, or the best solution?
Static pressure is the pressure you fill to and observe when the pump is off. Dynamic is the pressures you see when the circulator is running. You'd like to see positive pressure in all parts of the system when it is running. The pump head added should show up in the gauges.
Here is a graphic showing how the expansion tank connection affects the pressure in the system.
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me
A system with the restriction you have has to pump away from the expansion tank. You do not have that now.
You want the system restriction to be on the discharge side of the pump not the suction side