Replacing Old Heat Timer EPU (Red Board?)...EPU-D, Platinum, Tekmar?
MJW
Member Posts: 7
Hi All,
I help to manage a single pipe steam, 70 Unit apt building. We're looking to replace our trusty old Heat Timer EPU Control (Red outdoor sensor) with a new control.
Not sure that we need internet connectivity but variable clock and burner lockout via condensate return sensor seem to be worthwhile upgrades (though we are very rarely overheating).
The 60 minute cycle does work well for us. But I can imagine stretching the cycle length somewhat to 65 - 70 minutes.
And maybe having Day cycle start an hour later on weekends.
Does anyone have recommendations for the replacement control board between the Heat Timer EPU-D, Platinum, or Tekmar?
Thanks much!
- Mike
Rockmills 125HP Boiler/ Iron Fireman Dual Fuel Burner
I help to manage a single pipe steam, 70 Unit apt building. We're looking to replace our trusty old Heat Timer EPU Control (Red outdoor sensor) with a new control.
Not sure that we need internet connectivity but variable clock and burner lockout via condensate return sensor seem to be worthwhile upgrades (though we are very rarely overheating).
The 60 minute cycle does work well for us. But I can imagine stretching the cycle length somewhat to 65 - 70 minutes.
And maybe having Day cycle start an hour later on weekends.
Does anyone have recommendations for the replacement control board between the Heat Timer EPU-D, Platinum, or Tekmar?
Thanks much!
- Mike
Rockmills 125HP Boiler/ Iron Fireman Dual Fuel Burner
0
Comments
-
I would use a Tekmar I installed a few of those and they worked well and less $$$$$$ than a heat timer.
How about a picture of your Iron Fireman burner? I installed a lot of those. Out of business now.
!25 HP Maybe a C-240K gas oil burner. Just a guess. And that is if it is gas/#2 oil not heavy oil Heavy oil/gas would be a PAGO 6.3 or a AGO 6.3
0 -
One pipe or two?
Many Heatimer controls were installed on systems which were out of balance, and poorly (main) vented, so it would be wise to check on that part of the system at the same time.—NBC0 -
@nicholas bonham-carter, Single pipe steam. We have been fixing the distribution system over the last few years. Biggest addition were (2) antlers, (3) Gorton #2's each. And then many Gorton D's on distant radiators.
@EBEBRATT-Ed, Pictures attached of Iron Fireman C240-GO-SMK
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements