viessmann boilers

creger.robert
creger.robert Member Posts: 40
have viessmann model vb2-40 with riello burner lpg -is there a way to test primary control box 525
unit does not light on and off-if it lights it stays running.checked gas pressure ok. seems to be sparking

Comments

  • GW
    GW Member Posts: 4,832
    Trying a new primary box is simple and fast. Propane can be tough, moisture is tank and sticky regulators can soak you for time and energy. We had one Riello gas kick us hard once, had to walk away. That job had an undersized gas line, homeowner didn’t want to deal with it. 
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA