Munchkin F09 Error Code
Alan (California Radiant) Forbes
Member Posts: 4,214
We installed this Munchkin in 2006 and it's never been serviced. Received a call from the owner that his heat wasn't working with a F09 error code - "No flame detected". The burner would ignite and then go out right away. I checked the rectification probe, but finally pulled the cover off to see what was going on. While I was undoing the bolts, I looked over at the tridicator and saw that the pressure was dropping. It was then that I heard the sound of water running.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
1
Comments
-
-
-
Why never serviced?0
-
Time for a new boiler.....or find a old used hx...
What size is the boiler?0 -
The owner said that the boiler has never been serviced; curious because the house is fastidiously clean and neat and I've sent him my reminder postcards for servicing.
The boiler model is a T50M, Munchkin's smallest. Primary/secondary piping; heating only (no DHW).
We will be replacing the boiler, but the problem is finding a short one. The distance from the center of the flue to the bottom of the boiler is 27".
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I wonder what caused the hole in the stainless steel tubing? Can you tell if it started internally or externally?0
-
What does HTP have to offer? I thought those were lifetime warranty on heat exchangers.0
-
MikefromMn said:What does HTP have to offer? I thought those were lifetime warranty on heat exchangers.You can have it good, fast or cheap. Pick two0
-
I can't see how the heat exchanger leaking was caused by the no service. And 14 years isn't a "lifetime". If the heat exchanger wasn't leaking, I'd think a good cleaning & a new rear target wall would get it up and running.
Clogged drain from all the coffee grounds no doubt causing the F09. Amazing it ran as long as it did. I'll bet the owner reset it more than once.0 -
IMO, part of the cause would be the coffee grounds would have insulated the lower section of the HXC from transferring it's share of the heat letting the rest of the coil overheat.
These things need some serious water flow and have little mass to absorb extra heat. Just start one with the inlet/outlet valves closed and see how quickly you get a lockout.....how do I know this?
(Of course I was just testing the high limit)3 -
i understand this thought, and I guess if it's looking for a certain outlet temp and you aren't getting all the full heat absorption it's going to ramp up the flame compared to the actual load conditions.JUGHNE said:IMO, part of the cause would be the coffee grounds would have insulated the lower section of the HXC from transferring it's share of the heat letting the rest of the coil overheat.
These are cute reliable little boilers but I never like the credit card the junk into the sump and hope it is not clogged. They would be much more serviceable if there were a couple unions to get the heat exchanger out to work on it. I would keep these things going forever if that were the case (doesn't help them sell their new stuff I guess . . . not saying this was planned obsolescence so much as not thinking of the manufacturing engineer never thinking of the field engineer who has to service this stuff.).
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements