motor off delay

Options
xtrm4x4
xtrm4x4 Member Posts: 2
edited December 2020 in THE MAIN WALL
What are the benefits of the motor off delay? I have a Beckett Genisys controller.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,551
    It's called postpurge. It keeps the burner head cleaner by blowing air through the burner and exhausting it up the flue
    STEVEusaPA
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    Also prevents nozzle overheating and keeps everything nice and clean. the official term has been changed to motor or fan off delay
    STEVEusaPA
  • Steamhead
    Steamhead Member Posts: 18,193
    If you're using motor-off delay, you also need two "hot" wires feeding the GeniSys- one that goes through the safety limit controls and one that does not. If your unit already has this feature, great. If not and you're looking to upgrade, call a pro.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • xtrm4x4
    xtrm4x4 Member Posts: 2
    Thanks for the great info