another issue. Existing leaking rad is 6 tube by 5 section; standing 36" tall. No one makes that configuration. OCS, if buying new, indicating must go with a 6 tube 6 section but at 25" . Gentleman claims it won't heat room. Unit currently in corner, , 12 x 12 room- Uncertain what options could consider now?
0
Comments
-
Your existing radiator has an EDR of about 6 per section for a total of 30.
The 6 tube, 25 inch is going to have an EDR of 4 per section for a total of 24.
How does the existing radiator heat the room now? Just right? Too hot, too cold?0 -
it would say just right. it's piping is in the corner- in a 12x12 daughters room. no one has 36" ..AdmiralYoda said:Your existing radiator has an EDR of about 6 per section for a total of 30.
The 6 tube, 25 inch is going to have an EDR of 4 per section for a total of 24.
How does the existing radiator heat the room now? Just right? Too hot, too cold?0 -
I'm able to find a refurbished 5 tube 5 section for $600... is this good, size wise?0
-
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements