Tankless Coil Aquastat Settings?
EDIT: Changed L6006 to L4006
Depends if your good with the output of your hot water during the down cycle of calling for heat . Set at 180* with a 20 diff will turn on at 170* and shut off at 190*
We never have an issue with running out of hot water, though we do notice lower hot water pressure from time to time - which could just be the tankless coil showing some age.Big Ed_4 said:Depends if your good with the output of your hot water during the down cycle of calling for heat . Set at 180* with a 20 diff will turn on at 170* and shut off at 190*
Is 180 setpoint with 20 Diff a typical default setting? I am still not clear on how the diff works.
EDIT: Oops, I had the wrong model number before. Its actually an L4006A with setpoint and diff. Does this change anything?0 -
Following up. Can anyone answer my last questions? Thanks0
The adjustable differential is there to reduce short-cycling of the burner. I believe it adds to the temperature setpoint That means if you select the minimum differential of 10°F and you set the control at 180°F the burner will maintain a temperature between 170° and 180°. When the water temperature drops below 170° the switch contacts make and the burner operates. Once the water temperature reaches 180° the contacts open and the burner stops.
When you adjust the differential to 20° the new high limit is 190°. 10° more than the setpoint of 180°. The contacts close when the temperature drops below 170° and the contacts open when the water temperature rises above 190°. It is just a switch that turns on and off based on the temperature you select and the differential; you select.
Regarding the water pressure, you should have a mixing valve on the system. That mixing valve may be partially restricted. A good cleaning of the mixing valve and the tankless coil will bring the system back to optimum performance.
1 -
Further investigation reveals the differential is a "Midscale Differential". What this most likely means is that a setting of 180° and a differential of 5° would cause the actual high limit to be 182.5° and the cut in temperature is 177.5° to be determined by actual testing after installation.
If the differential is set at 10° then the 180° setting was actually 175° cut in and 185° cut off.
Set the differential at the maximum of 30° and the 180° setpoint and the high cut-off would be 195° and the low cut-in temperature would be 165°. This would also need to be verified by actual testing after installing the control.
The actual reading on the thermostats, controls, and thermometers have liberal tolerance. Testing is the fail-safe of the installing technician. Just installing the part without verification is not good practice.Edward Young Retired
1 -
Thanks. That is all very helpful. What are some good default settings I should start with and then tweak based on the results?0
I would start at 160° setpoint and 10° diff and see if you have enough hot water. If so your off-cycle loss will be less at 160° than at 180° setpoint. The lower the minimum temperature the less fuel you will use. But don't give up comfort for a few dollars in savings.
1 -
Since it’s usual for incoming cold water to be colder in the winter and warmer in the summer, you may find that you can use a lower aquastat setting in the warmer months.—
Bburd0 -
Have my setpoint at 160 with a diff of 10 and water temp is perfect coming through my mixing valve. I also took apart the mixing valve and cleaned it out though there was not much build up. What's the best way to flush my coil? I've read about pumping in a vinegar mix but any other options?
Somewhat related question - the water pressure entering our house is ~80 psi which I understand to be a bit high but not crazy. Is it worth installing a pressure reducing valve at this pressure? And if I do, do I need an expansion tank for my coil?0 -
To make a short answer LOOOOOONG
A pressure reducing valve PRV set at say 50 PSI would be a good idea for all the valves and fixtures on the system. less stress on the moving parts... "Yada... Yada... Yada..."
If you have a PRV you should install a small expansion tank for the same reasons as the PRV (all those Yadas above). As the cold water from underground piping enters the home and warms up to room temperature, it will expand and increase pressure if there is no place to go. You see the PRV acts like a check valve and will not allow the expanding water to flow back into the water company piping system (backward thru the meter.) Your water meter may also have a backflow preventer connected for that same reason.
Also, the water in the tankless coil will expand once the hot water valve, tap, or washing machine solenoid valve closes. Since there is no "top of the water heater air cushion" to accept this expansion, and in many cases, there are no relief valves on tankless coils (I could never figure out why that was not enforced) the pressure exerted on many faucets and valves can be tremendous. But it goes away as soon as someone opens a valve (like the ice maker on your refrigerator).
Regarding the tankless coil cleaning, There are 3 that I have used successfully. All three require that you have isolation valves on the hot and cold water side of the coil and a boiler drain valve on either side of the coil between the iso valves and the coil. This way you can flush the mess out of the pipe without putting any of the debris into the rest of the hot water system throughout the house... clogging up all the little strainers.
After the valves are in place you can try the first one. It is free.
1 Shock the crap off
A. First, you need the get a garden hose about 3 to 5 ft long (Washing Machine connector works well)
B. You also need a 5-gallon pail.
C. Connect the hose to the boiler drain of the hot outlet of the coil.
D. Set all thermostats in the home to off or the lowest temperature. No calls for heat. and record where the aquastat settings are.
E. Set the boiler high limit to 235°
F. Set the low limit to 225° Turn on the switch to operate the burner.
G. Once the boiler temperature is at 225° let the water in the tankless coil absorbed the heat for a minute or so.
H. Place the free end of the garden hose in the 5-gallon pail. You may want to have something to clamp the end of the hose so it stays in the bucket.
I. Close the cold water inlet to the tankless coil and then open the boiler drain on the hot discharge. The water pressure in the coil will drop to atmospheric pressure and the water in the coil will flash to steam shocking off a significant amount of crud and crap.
J. within a few seconds, after the pressure is released, open the cold water supply to the coil and shock the coil again with cold water against the hot copper inside the boiler.
K. close the boiler drain to the 5-gallon pail after the water runs clear.
L. Empty the bucket and let the boiler heat the water in the coil for about 10 minutes.
M. Repeat steps H thru L for a total of 3 flushes.
2 Acid the crrap off
A. Shut off the hot and cold water valves to the coil
B. Open the boiler drains
C. Connect hoses to the boiler drain valves and place one in the 5-gallon pail.
D. Using a hand pump or standpipe apply 1 part Hercules Sizzleand 2 parts water into the coil until it runs out the other side drain valve.
E. Let it sit until foaming stops.
F. Add more sizzle as needed.
G. Adding more sizzle with no foaming means the coil is clean.
H. Flush the coil with cold water of all the chemicals and run water out the hot water drain for 5 minutes after the chemical has cleared.
I. Use the enclosed test to be sure the water is at the proper pH before opening the hot water isolation valve.
J. Flush all the hot water faucets for about 2-3 minute each, to be sure all the chemical is gone from the system before drinking, cooking or showering.
Caution this acid may cause the copper pipe to fail if the corrosion is extensive. You may need to replace the coil after procedure #1 or #2 ...but that would happen soon anyway without cleaning.
3 Maintain the crap off
Use vinegar-based cleaner or tankless coil cleaner on a regular basis (annually or bi-annually) depending on your water condition. Here is a good kit to use.
Do NOT use this setup with Hercules Sizzle.
https://www.homedepot.com/p/Flush-Kit-for-Tankless-Water-Heaters-RTG20124/202798886?source=shoppingads&locale=en-US&mtc=Shopping-VF-F_D26P-G-D26P-26_10_WATER_HEATERS-MULTI-NA-Feed-PLA-NA-NA-WATER_HEATERS&cm_mmc=Shopping-VF-F_D26P-G-D26P-26_10_WATER_HEATERS-MULTI-NA-Feed-PLA-NA-NA-WATER_HEATERS-71700000033150351-58700003868932468-92700049176334365&gclid=Cj0KCQiA0fr_BRDaARIsAABw4EsPV0QrLRg3tH2mAAVNnek6EmkJyLi7ijANsrQOy1AHT4Bi7RsOujIaAvjIEALw_wcB&gclsrc=aw.ds
Yours Truly,
Mr.EdEdward Young Retired
1 -
1 -
Wow - lots of information for me to digest. Thank you. I will note my boiler is steam so I don't quite have the temp control abilities mentioned in cleaning option 1.
Would I need an actual expansion tank or would a large water hammer arrestor like Watts 150A suffice? Also, where on the system would the expansion tank go? I know my mixing valve has check valves on both the hot and cold inlets.0 -
Following up on my last post.
"Would I need an actual expansion tank or would a large water hammer arrestor like Watts 150A suffice? Also, where on the system would the expansion tank go? I know my mixing valve has check valves on both the hot and cold inlets."
As far as cleaning, think I'll probably wait until summer when I won't need the boiler for heat since I'll need to add valves to connect the hoses to the coil etc.0 -
Wanted to follow up here again @EdTheHeaterMan0
You have a steam system. So there is no expansion tank... and... you can do step #1. Keep in mind that the water pressure in the coil is separate from the steam pressure in the boiler. There is a wall between the two waters The steaming water is in the boiler but on the outside of the tankless coil. The potable water is on the inside of the tankless coil so it is still under pressure and will not boil when the boiler is steaming. Once you open the purge valve to let the water pressure out, the shock will happen and break off the deposited inside the coil. I will need to rewrite the instructions for steam boilers (the instructions given are for hot water boilers)
That is what happens when you just copy and paste without reading the information.Edward Young Retired
Here is the revised instructions for a steam boiler.
D.Set all thermostats in the home to off or the lowest temperature. No calls for heat. and record where the aquastat settings are.Turn on the switch to operate the burner. and jump out the thermostat or turn it up to 90°
G. Once the boilertemperature is at 225° begins to make steam, let the water in the tankless coil absorbed the heat for a minute or so.
Thanks for the updated instructions @EdTheHeaterMan. I obviously don't have high or low limits, so that's the part that didn't make sense to me.
Still looking for an answer to these questions if you don't mind. This is in reference to me adding a PRV on the system.Would I need an actual expansion tank or would a large water hammer arrestor like Watts 150A suffice? Also, where on the system would the expansion tank go? I know my mixing valve has check valves on both the hot and cold inlets.
No need for a pressure reducing valve on steam boilers. The PRV would be for the whole house potable water... so just after the meter is the best location. The location of expansion tanks is a question for the plumbers herein. I would say that you need it near the tankless coil, between the coil and a check valve that will not allow for the release of pressure because the water can not reverse past the check valve.
You also need to provide for expansion anywhere there is a valve that prevents the release of pressure in reverse to any other expansion allowance device, meaning you may need more than one if there are multiple check valves and backflow preventers. This is where you have to think like water in your mind's eye and say "If I were water where would I go if heated?" If there is no place then you need to make a place.Edward Young Retired
Yes, I understand where the PRV needs to go. I just don't know where the expansion tank needs to go. So if anyone else might be able to answer, it would be much appreciated.0
The more I think about it, the only logical place is after all the check valves. As water expands from heating, it needs a place to go. it will go thru the check valve to the next check valve and the next check valve to the expansion tank. Then as it cools it will shrink. Not such a big problem. It will never cause a vacuum because the city water pressure will fill the void. We want to stop extreme hydraulic pressure so the best place is on the mixing valve's Mix water out port to the faucets. The tank's air cushion will take up the pressure and compress as the water expands. As soon as a hot water tap is opened, then the tank will reset to the tank charged pressure. That should be set to the PRV pressure setting.
@hot_rod or @Youngplumber should be able to verify the potable water expansion tank location. I'm an oil heat and Hydronics guy.
Respectfully submitted,
@hot_rod @Youngplumber any advice?
Also, an additional question about bonding. I know tank water heater typically requires a bonding wire across the hot and the cold. Is the same required for a tankless coil or no because the coil itself is continuous?0 -
@Youngplumber
a PRV acts as a check valve0 -
OK looks like the other guys are not answering the DHW expansion tank location query. I believe you need one and I believe the location should be just after the mixing valve on the pipe coming out to the MIX port. Anywhere on that pipe before any shut-off valves. This way the expansion tank is always connected to all the possible factors that can expand the water.
Does that make sense?
Regarding Bonding the Hot and Cold together. As long as you are not using insulated dielectric unions on the hot and cold connection, the bonding is not necessary. https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Zurn-112-DUXLC-Product-Overview.pdf
@Youngplumber Well I think I may be more confused now unfortunately. Can you expand on what you mean by not just adding a t? Most/all of the examples I see online for potable water expansion tanks are on a t.
I was adding shutoffs and drain valves over the weekend so I can flush the coil, so I added the expansion tank on the mix on a t(prepared to change it if I have to). Here are so pics of what I have now, let me know your thoughts.
It is in the correct location.
Great thanks! Thoughts on my tankless flush setup @EdTheHeaterMan ?0
Looks right to me! That is basically how I would have done it.Kafox15 said:Great thanks! Thoughts on my tankless flush setup @EdTheHeaterMan ?
Are you going to try to Shock it first or did you order the acid?
The acid option worries me a bit, especially in the dead of winter. Likely going to try the shock method and maybe a few rounds of vinegar flush before resorting to acid.EdTheHeaterMan said:
Are you going to try to Shock it first or did you order the acid?0 -
Good choice. The vinegar cleaning will take time. Maybe several doses over a day or two. Purchase 2 or 3 gallons of vinegar and use about 1/2 of a gallon per flush and operate the pump for about 30 minutes per flush. It's kind of like cleaning out the coffee maker with vinegar after months of boiling water You have Years of buildup.Kafox15 said:
Yours Truly,
Mr.Ed
@Youngplumber So I installed the PRV over the weekend and now I am running into some flow issues. Let me know if I should start a new thread since this is wandering away from the original topic.
Wondering if I may have done something wrong or if our high-ish pressure (80psi) was masking our flow issues and now its just more obvious at a lower pressure.
The PRV is a Watts LF25AUB-Z3 3/4" and came set for 50 psi. Reduced flow was very noticeable at all sinks and made the 2nd floor shower almost unusable. I upped the setting to about 60 psi and its better but still not great. Cleaned the aerators on faucets and showerheads and even the PRV screen but no improvements.
As a test, I attached a pressure gauge to the 2nd floor sink and opened the cold tap. Static pressure was ~60 psi. Opened the cold tap on the adjacent shower and the pressure dropped to about ~40. This seems like a significant drop for a shower valve that has a rating of 1.8gpm.
I know there are tons of variables here, but if anyone has any suggestions on other things to check or test, please let me know.
Yea I get the drop is going to happen but I just thought 20 psi drop was excessive for one fixture. I was testing with just cold to avoid too many variables.
House is old, early 1900s. Supply from town is 3/4 copper and all copper piping in the house.
Flow restriction sounds likely, but where do I start to track it down?0 -
The shower is the "worst" but probably just because that's where we want the most volume. So I guess its subjective. Flow is noticeably worse at all fixtures since installing the PRV. I have limited access to the shower valve from the other side of the wall but nothing looks off. No leaks but there are no valves here. I exercised every single valve in the basement and none are partially closed.Youngplumber said:What fixture is the worst. The shower? Is there a way you can look at the piping (to the shower)? A valve somewhere that is partially closed?
How bad is the lack of volume everywhere? Where besides the shower do you need more volume? One shower?
We would like more volume everywhere but could live with the others if the shower was better. We have two showers but only this one is used.
Soft copper is exactly what we have in some spots. The supply from the town comes in through the foundation, goes through the meter and then immediately dives under the basement slab. Comes back up on the other side of the basement where it connects to the PRV and then off to any fixtures/appliances. I believe only the part that goes under the slab is soft copper since its curved where its visible. No kinks/leaks in any visible sections but who knows what under the slab.Youngplumber said:In older homes especially remodeled ones plumbers used soft copper to fish piping into places. Could be partial kink.
I did remove the flow restrictor from the shower head yesterday and it actually made the flow worse so I put it back in. Both the shower head and the valve are rated for 1.8gpm so even if we could increase shower head flow, we are limited by valve.Youngplumber said:I forgot to mention the whole low for shower head possibility. It may be possible to remove the restriction in the shower head if it is a low flow assembly.
Yea, I understand that the flow will be lower, but I just didn't expect it to be this bad. I will do a test to see what gpm we are actually getting out of the shower, but I would think 60 psi would be enough to max out the 1.8gpm rating, no? That's why I think there must be a restriction somewhere.
3/4 feeds some branches but not all. Some step down to 1/2 before branching off. I'm trying to rule out other possibilities before I undertake replacing large sections of pipe.0 -
Hi, I'll add that you can get pressure compensating shower heads. They will give essentially the same flow between 20 and 80 psi. Look up Neoperl if you have a problem locating the right head. Neoperl makes the pressure compensating parts for most of the manufacturers, so they will know.
Yours, Larry0 -
Nope, the cold steps down to 1/2 before it branches up to the bathroom and the hot is entirely 1/2 since thats how it comes out of the tankless coil. At this point, I'm feeling as though the PRV was a mistake.Youngplumber said:With lower pressure there should be 3/4 feeding the 1/2 lines. Is that the case for the problem shower?
I'll look into it. Its just a cheapo three handle home depot model.Youngplumber said:It might be worth investigating whether or not your shower valve has a cartridge with a larger gpm output that could be changed out.
I think ours might already be that considering flow got worse when I removed the flow restrictor but I'll do some research.Larry Weingarten said:Hi, I'll add that you can get pressure compensating shower heads. They will give essentially the same flow between 20 and 80 psi. Look up Neoperl if you have a problem locating the right head. Neoperl makes the pressure compensating parts for most of the manufacturers, so they will know.
Yours, Larry
I've got everything to an "acceptable" level by upping the PRV to 65 psi. Not ideal but I think it will be fine.
I've also ordered some shower cartridges to see if I can find one that offers higher flow. Might just be time to finally upgrade to a modern single handle shower valve and use one of those remodel plates to cover the giant hole it would make.
Thanks again @Youngplumber and I'll let you know if I have more questions.0