flo check problems

Joseph_4
Joseph_4 Member Posts: 293
I had a customer last yr with 3 zones via pumps and was getting ghost flow in another zone making very hot. he had no flow check so i installed 3 cast iron flow checks.. It fixed problem for rest of season. now he is having problem again.. I cant believe the flo check valve went bad.. Any advice what to look for? I can install zone valve on that zone which would be a sure fix ( or replace that flo check on that zone) but he is upset.. I would be too if i were the customer.
Thank
Joe

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited November 2020
    Three things
    1. most unlikely, but the valve may have failed. There could be a piece of debris keeping the valve from closing.
    2. ghost flow from the return, (or the supply if you installed the flow check on the return). this is more likely the larger the pipe diameter.
    3. circulator is operating all the time. Check the relay.

    Read the discussion starting on page 10 of this publication from B&G
    https://documentlibrary.xylemappliedwater.com/wp-content/blogs.dir/22/files/2020/01/FH-Z100B-BG-Zoning-Made-Easy-2.pdf

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Joseph_4
    Joseph_4 Member Posts: 293
    Thanks so much.. the advice u gave me for the 2 wire feeder worked like a charm
    thanks
    Joe
  • Baggypolo
    Baggypolo Member Posts: 4
    What was the advice about the two wire feeder? I have the same issue.