Utica PEG-C boiler does not consistently fire up
don2347
Member Posts: 3
I have a Utica PEG-C gas fired steam boiler that sometimes needs some help to fire up. When the boiler does not fire up on its own, I find that I can pull and press on the wires connected to the Honeywell S8600M intermittent pilot control. This will cause the pilot to light and the boiler to work properly. The problem is intermittent. So far this season, it has failed to start on its own two or three times. Pushing the wires into the pilot control is usually enough to get the boiler started, although last winter it sometimes took a little more tugging and pushing. I am wondering if the there is a safety feature causing the boiler to not start that points to something more serious than a bad wiring harness or pilot control.
0
Comments
-
You may just have to replace the Honeywell S8600M, but before you do, check to make sure you have a good ground. The internal relays get tired and often go bad.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
This.You may just have to replace the Honeywell S8600M, but before you do, check to make sure you have a good ground. The internal relays get tired and often go bad.
Sounds like there is a bad soldered joint on the PC board in the control. Honeywell makes a universal replacement for this, that any competent heating contractor should have in stock.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I have had similar problems in past and solved it by replacing the Thermopyle. Over time the thermopyle continued to get “weaker”.
0 -
This system uses electric ignition- there is no thermopile.Portgas said:I have had similar problems in past and solved it by replacing the Thermopyle. Over time the thermopyle continued to get “weaker”.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks for the comments. I followed the ground wire connection and it looks good. I see that Honeywell S8600M has been replaced with universal part S8610U.0
-
don2347: i have the same boiler and replaced my control panel with the universal one last year for a different issue. Works great.0
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements