Honeywell RedLINK Wireless Thermostat System
Alan (California Radiant) Forbes
Member Posts: 4,243
I installed one of these in 2012 and it has worked flawlessly, but I remember being surprised that the zone panel didn't have an end switch to turn on the boiler. I had to add a relay for every zone. Have any of you figured an alternate way to find a dry contact as I have another install coming up?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
-1
Comments
-
I’m confused, wouldn’t you just use the W ouput from the zone panel to call the boiler? The boiler I assume has a pump relay already on it. Don’t really need end switches if you use a ECM circulator and a differential bypass.0
-
RH and W are a dry contact if you remove the jumpers
There was an error rendering this rich post.
0 -
RH and W are a dry contact if you remove the jumpers
I always thought that if you remove the jumper, only Rh is connected to the transformer. The jumper is removed when the a/c unit has its own transformer.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
motoguy128 said:I’m confused, wouldn’t you just use the W ouput from the zone panel to call the boiler? The boiler I assume has a pump relay already on it. Don’t really need end switches if you use a ECM circulator and a differential bypass.
@Alan (California Radiant) Forbes, I don't see why a set (or 2) of dry contacts can't be incorporated into the zone panel. It can do almost everything else. Its not just HW, I haven't seen that option from any manufacturer. We install a GP relay in the air handler, W from Equipment on the panel energizes the coil and closes TT (RW) at the boiler relay.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements