Preheating tankless WH or combi with solid fuel boiler
GroundUp
Member Posts: 2,076
Super dumb question: will a tankless or combi boiler recognize the hot inlet water and resist firing if the water was preheated with a plate HX in a wood boiler loop? I do this all the time with heat-only boilers, with the TT interrupted by an aquastat on the OWB supply line, but with a tankless or combi operated by a flow switch I'm not sure what the proper channel is. Has anyone done this? The application in question is a Lochinvar Noble 110, but I can't imagine there would be much difference with any other tankless. TIA!
0
Comments
-
Why wouldn’t you just dump the hot water from the boiler into a storage tank?
There was an error rendering this rich post.
0 -
Because he doesn't want a storage tank, he wants a combi.0
-
I feed my Cadet and Nobel pre-heated water, either from the solar or wood boiler. If the pre-heat drops below 110°F the Nobel fires up.
The flow switch always "makes" when it sees .5 gpm or more, but the burner will stay off on temperatures.
If you feed it say 90°, the combi kicks on low fire to make the difference to 120° or set point.
I have heard of excessively high temperature from a wood boiler to the mod con, boiler side, depending on piping tripping a high limit. See if yours has an automatic, or manual reset high limit.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Hi, Tankless gas heaters don't often do well with preheated water if they have thermostatic controls. Electric tankless can do better. A problem happens when the supply water is close to the desired temperature because tankless gas cannot heat it just a little. Something with a big burner and a small tank (like the HTP Crossover) would probably do better.
Yours, Larry2
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements