Heat pump aux heat to zone relay
skippy76
Member Posts: 4
I have a heat pump setup with Neat thermostat. All works great, heating and cooling. The air handler does not have any aux heat / emergency electric coils.
I have installed a hydronic coil to the air handler to connect as zone 3 on the hydronic heating system. Each hydronic zone has its own pump controlled by a Taco 503-4 zone relay.
I wired the W1 (alternate heat) from the Nest to the W on Zone 3 and the C on Zone 3 to the C in the air handler. Note that R on zone 3 of controller is not connected.
When the thermostat calls for Aux heat I see voltage between W1 and C, but zone 3 does not activate.
Thoughts?
I have installed a hydronic coil to the air handler to connect as zone 3 on the hydronic heating system. Each hydronic zone has its own pump controlled by a Taco 503-4 zone relay.
I wired the W1 (alternate heat) from the Nest to the W on Zone 3 and the C on Zone 3 to the C in the air handler. Note that R on zone 3 of controller is not connected.
When the thermostat calls for Aux heat I see voltage between W1 and C, but zone 3 does not activate.
Thoughts?
0
Comments
-
R and W from zone 3 in the SR503 go to Rh and W on the Nest. The Nest will recognize it. Remove the Common you added. What activates the fan with the hydro air? If you didn't install an aquastat then set the Nest to bring the fan on.0
-
Thanks. The Nest activates the Fan.0
-
Thanks again, this resolved my issue. I now have hydro air for when it is more efficient / not possible to run the heat pump.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements