Venting a Viessmann 200 boiler
TAG
Member Posts: 757
What do most people use to vent Viessmann wall boilers. Single pipe exhaust?
It seems the contractor hired by my previous builder used 3" PVC -- this by way of Viessmann is a no go. The new guys were surprised at the cost of CPVC and don't really like it anyway. Some problems getting the OE Viessmann from the distributor that sells Viessmann products ... due to supply. Great. The exhaust goes out the roof -- but, the intake vent will come in from a side wall. Viessmann seem Ok with PVC there. It seems that nothing is cheap ---- told the installers I will pay for whatever the cost. Two story addition with cathedral ceiling .. the boiler was picked based on the distance of this exhaust. One of the Bosch unit did not work w/ flue length.
My project has been in the works for years. Major fire. After fighting Insurance and township my architect ended up telling me to fire my builder just before all the rough services went in .. ended up with a lot of bought equipment (boiler etc). Getting a new builder when you fired one is not an easy task and I almost sold the property out of cost and frustration. Anyway -- it took another two years -- Found a good one and the HVAC guys have done a great job with a complex system and install. The PVC was done by the last guys as the roofers doing the metal roof needed a pipe .. never a dull moment ! I'm suprised they used the wrong stuff as they install Viessmann boilers?
It seems the contractor hired by my previous builder used 3" PVC -- this by way of Viessmann is a no go. The new guys were surprised at the cost of CPVC and don't really like it anyway. Some problems getting the OE Viessmann from the distributor that sells Viessmann products ... due to supply. Great. The exhaust goes out the roof -- but, the intake vent will come in from a side wall. Viessmann seem Ok with PVC there. It seems that nothing is cheap ---- told the installers I will pay for whatever the cost. Two story addition with cathedral ceiling .. the boiler was picked based on the distance of this exhaust. One of the Bosch unit did not work w/ flue length.
My project has been in the works for years. Major fire. After fighting Insurance and township my architect ended up telling me to fire my builder just before all the rough services went in .. ended up with a lot of bought equipment (boiler etc). Getting a new builder when you fired one is not an easy task and I almost sold the property out of cost and frustration. Anyway -- it took another two years -- Found a good one and the HVAC guys have done a great job with a complex system and install. The PVC was done by the last guys as the roofers doing the metal roof needed a pipe .. never a dull moment ! I'm suprised they used the wrong stuff as they install Viessmann boilers?
0
Comments
-
-
-
Poly is the only logical choice of the Viessmann approved materialsTo learn more about this professional, click here to visit their ad in Find A Contractor.1
-
I think the Bosch Greenstar was the one with a shorter Flue length -- The Bosch/ Buderus was fine. I was hearing of many problems with the ....142 I think is the model. I went with the Viessmann .... I also heard from a few people it was an excellent boiler on propane.
Thanks for the pipe recommendation --0 -
We use Centrotherm thin wall polypropylene, we two pipe it. Don’t use concentric like the old says0
-
Centrotherm polypropylene all the way. Very light and easy to use although strapping it securely often takes longer than running the pipe.
A few years ago, it was hard to find a local supplier and I had go out of state. It's better now.
Here's their catalog:
https://www.centrotherm.us.com/getmedia/4cf931d2-09fe-4430-a61f-90dab777c8d1/Centrotherm-2019-Catalog_2.pdf.aspx8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Thanks -- I passed on the information. Sometimes is easier to have some direct answers to what works .... VS having choices.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements