Gas boiler troubleshooting
jsilva2
Member Posts: 3
in Gas Heating
Hello, I’m hoping some can help me figure out why my gas boiler won’t fire.
I have a New Yorker gas boiler, baseboard heat with two zones. One circulator pump and two taco zone valves. I have set both thermostats to heat and I’ve set them both well above the room temperature but the boiler does not kick on. There is no voltage at the circulator pump. The exhaust damper does not open. I have a zero volt reading on the spill switch and zero volts on the roll switch. All of the terminals on the low water cut-off read 115v except for furthest right which reads 0v. I also have no power to the aquastat. I have tried switching the damper to manual and opening manually and I have tried adjusting temp on the aquastat both resulted in no change. I have good pressures on both the expansion tank gauge and boiler gauge. The pilot is lit. I have attached some pictures if anything helps.
0
Comments
-
If you have voltage between the black and white in the low water cut off but none between Red and White, the problem lies there . Is there a jumper from Black terminal 2 to terminal 3 ? If yes .... Either a bubble is trapped in the lwco piping ,, or the lwco if bad ..
I don't see an jumper ...
There was an error rendering this rich post.
0 -
Thank you it’s hard to see in the picture but there is a metal jumper plate between terminals 2 and 3 and I can measure 115 volts on both terminals.0
-
Are the zone valves open? They're on a separate transformer on the side of the boiler. Is there 24v at that transformer? If the valves are open, or you can manually open, try jumping the end switches. At that point there should be 24v between G and C at the boiler control relay. If yes then check for 24v between Y and C. That's the circuit that goes through the safeties and ends at the gas valve. If no 24v between Y and C, then the relay is faulty. Just pop the clip and pull it out. Turn off the power first.1
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements