Position and purpose of Valve

What is the purposed of this valve in the picture? (The Shut Valve) Is shut the normal position?
Thanks.

Thanks.

0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 561 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
Completely closed it does nothing. Completely open your house will never warm up.
It’s the worse way and not the best choice of valve to protect the boiler. You, or someone will have to figure out how far to open it to find the sweet spot.
And as time goes by and wire drawing starts to ruin the valve you’ll have to adjust it again.
To know, measure the temperature coming back to the boiler on the first, cold start up, all zones running. Within 10 minutes that return should be around 130F.
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me