American Radiator Company, Ideal No. 7 boiler
I'm also a be concerned about the amount and placement of asbestos this unit has. Info on this would be greatly appreciated. pic attached.
Comments
-
@Steamhead is good with these, but looks to me like it could use some baffles and a good tuning using a combustion analyzer.
Is there a barometric damper on it?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Don't worry about the asbestos unless you goof with it, leave it alone. When it's time to replace the boiler call a company that specializes with asbestos removal and let them deal with it. I would cut the old boilers lose that had asbestos and push it out of the way. The last one I did the home owner made the call to a company and they showed up and wrapped the boiler in plastic and carried it out in one piece.0
-
It has had its day. Probably only 40% efficient overall. That means 60% of the money you are spending on oil is going up the chimney.
A modern efficient oil boiler will be more comfortable, more efficient and save you money along the way.
I don't like the way the air tube is sitting in that chamber. Looks like it's prone to over heating and will burner off. Needs some work.
Through proper combustion practices, you will at best probably only get to a 1 smoke, any less will require too much excess air.
Also the 2 upper doors are going to need to be sealed properly.
And as @ChrisJ mentioned, proper over fire draft controlled with the correct barometric damper is a must.
There was an error rendering this rich post.
2 -
The one my neighbor had tested in at over 70% efficient. It's a 3 pass.STEVEusaPA said:It has had its day. Probably only 40% efficient overall. That means 60% of the money you are spending on oil is going up the chimney.
A modern efficient oil boiler will be more comfortable, more efficient and save you money along the way.
I don't like the way the air tube is sitting in that chamber. Looks like it's prone to over heating and will burner off. Needs some work.
Through proper combustion practices, you will at best probably only get to a 1 smoke, any less will require too much excess air.
Also the 2 upper doors are going to need to be sealed properly.
And as @ChrisJ mentioned, proper over fire draft controlled with the correct barometric damper is a must.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I would recommend replacing the end cone with a F-5 . Its best to stay with in the range , rather than being on the end of one . Looks like it starting to distort anyway. From heat for sure . They need a new chamber. If they caped the chamber when it was replace it would not have cave in like it did .
There was an error rendering this rich post.
0 -
-
At the bare minimum, it needs a bathtub chamber rated for 1.25 GPH, an amulet to protect the air tube, and an F6 head. Adjust as best as possible using an analyzer and smoke pump.
The stuff around the chamber is not asbestos. It looks like vermiculite. Which was typical in the stone age. In some areas it did have small quantities of asbestos. But I think that came later.1 -
-
On that boiler, if the flue passage sizes are what I think they are, I'd use bricks to baffle the boiler. You want to slow down the escaping flue gases and make them transfer more of the heat to the cast-iron. But you do NOT want to restrict the flue passages enough that you create positive pressure in the firebox. And your stack temperature should be above 300°F to avoid flue gas condensation.ChrisJ said:@Steamhead is good with these, but looks to me like it could use some baffles and a good tuning using a combustion analyzer.
Is there a barometric damper on it?
And, what @STEVEusaPA said about the air tube and head sticking into the firebox.
What size (front-to-back, side-to-side, depth) is that firebox?
Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Long Island, NY
0 -
thanks all for advise. I have a situation with this system.
I have a B&G 107019, 1-1/4, flo valve that makes the clunking noise when system call for heat is turned on. I am considering on replacing, I started to drain for job. halfway through draining, i got the clunking sound, i'm thinking the water was flowing backwards, creating clunking sound. judging by this, water direction, it make noise both directions, I'm thinking the valve is no good. also, the lever is rusted shut, can't turn. and can open bottom to clean either.
the reason for this is one of these loops tend to fill with air constantly. I bleed multiple times per season.
there doesn't appear to be any air separator in the system either.
0 -
What kind of expansion tank do you have?0
-
Post some pics of the whole system, from different angles.
If it's just one flo valve rattling, there could be air in that loop or the weight in the flo valve is not seating properly.
How do you bleed the system? At the rads or are there purge stations at the boiler?
Pressure is correct?0 -
I'm taking the advise on repiping. this is what is my layout. didn't connect everything yet.
all black pipe is 1-1/4. started with 18 rise, then shutoff valve (wondering if this is appropriate), new temp/press gauge, 18 horizontal run, air scoop, flow control, 3 port header.
I believe this is all it the correct order.
will be adding drain valves on the return side.
thoughts
0 -
i'm connecting the black pipe with both teflon tape and blue monster pipe dope. and tightening connections really tight.
Can you over tighten black pipe? how do you know when its good enough?0 -
Is that the right expansion tank? Should have a perchance of 12 psi, I'd check it. Tank looks to be a domestic hot water x-tank.
If it were me I would have not bought a new flo-check but rather do a new IFC circulator with a built in flo-check. If you have a 3 piece circulator that would be the automatic choice.
Temp gauge on the header wi only be accurate when pump is running.
0 -
Probably underfired looking at the fitting size coming out of the boiler. Maybe that is why it won't heat the house.0
-
@EBEBRATT-Ed; could you elaborate? 1-1/4 is one of 2 supplies. it appears this is a converted steam boiler, the second output is 2". i don't understand how that effects heat supply when it all gets reduced to 3/4 as it feed baseboards.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements