Type "W" Oil Burner Nozzle
Thanks for any input on this.
Jay
Comments
-
Doesn't work that way. The W is sort of a cross between a hollow (A) and a solid (B) which is also known as a "semi". It's handy to have but won't satisfactorily replace either.
Our company stocks a selection of all three types.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting4 -
Unfortunately there's no way to cut down on the need for a wide variety of all three types of nozzles. Its best to stick with the spray pattern that the boiler is designed for.
I've used W nozzles in place of A and B nozzles when I'm in a jam. But i I always make sure I have a true zero smoke and my combustion analysis meets the manufacturer's specifications. And I always go back to the correct nozzle next chance I I get.1 -
I only use W nozzles ,B's if I ran out of W's . In my area with corn oil added , the W works the best ...The angle depends on the Boiler and burner . I stay what the manufacture posted on a tuned boilers like a Buderus ... Pin boiler , I prefer to dropping size and increasing pump pressure to stay in the firing range , to get that bright clean fire ...
There was an error rendering this rich post.
0 -
Beckett, Riello, and Carlin all have OEM spec books or downloads for numerous burner and boiler combinations. The W nozzle is not all purpose. Its specific to the application. I have been known to use one when I wasn't getting good numbers with a spec'd A or B. Sometimes you need to do a field bench test. I did work with a guy who used a W on everything. He also put a Carlin EZ-1 head on a 99 CRD once, on an original Blue Ray, so there's that.
2 -
Corn oil??Big Ed_4 said:I only use W nozzles ,B's if I ran out of W's . In my area with corn oil added , the W works the best ...The angle depends on the Boiler and burner . I stay what the manufacture posted on a tuned boilers like a Buderus ... Pin boiler , I prefer to dropping size and increasing pump pressure to stay in the firing range , to get that bright clean fire ...
To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
This. The more an OEM spec is different from the retrofit spec, the more likely you'll be giving your analyzer a workout.HVACNUT said:Beckett, Riello, and Carlin all have OEM spec books or downloads for numerous burner and boiler combinations. The W nozzle is not all purpose. Its specific to the application. I have been known to use one when I wasn't getting good numbers with a spec'd A or B. Sometimes you need to do a field bench test. I did work with a guy who used a W on everything. He also put a Carlin EZ-1 head on a 99 CRD once, on an original Blue Ray, so there's that.
To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Here are some links to Delavan's nozzle literature.
This one actually diagrams the various spray patterns:
https://assets.delavan.com/delavan-oil-burner-nozzles-and-accessories.84l1k9.pdf
This one goes into a bit more detail:
https://assets.delavan.com/241863-delavancx3.i6jp2a.pdf
I'm not sure why Delavan calls the W an all-purpose spray. Either the nozzle spray pattern matches the air pattern of that particular burner in that particular boiler, or not. If not, you won't be able to tune the burner properly.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks everyone for your input on W Nozzles - Jay0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements