Jet pumps in series or parallel?
Timco
Member Posts: 3,040
I have a 3/4hp 12GPM jet pump pressurizing my irrigation main and I need a bit more flow. I cut a floor mount B&G inline and it worked great but it’s not exactly the same size. I’ll buy an identical pump but what’s the performance difference for pumps In series or parallel?
Just a guy running some pipes.
0
Comments
-
Parallel doubles the flow rate with the same discharge pressure.
Series is in fact a 2 stage arrangement, so this increases the discharge pressure, but not the flow volume.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.1 -
Got adequate pipe size to move the extra gpm? Doubling the pumps will provide more flow. More flow through the pipe raises the head of course, so you may not double the flow at the end of the line.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
This is what I Did and it really throws better now! It’s all 1” system. Some zones have 8 heads at 3gpm each so I need better delivery in those zones. It’s how we bought it. I added the red pump today.
Just a guy running some pipes.0 -
24 gpm would be a lot to shove thru a 1" pipe. But if you are getting the sprinkler coverage you need with the series pumps, that is the win.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I’ll never get 24GPM but better is acceptable given the alternative. My wife has me adding some heads too. What I can’t wrap my head around is pressure vs flow or series vs parallel. I’m running the pressure switch to 60psi. If I’m looking for more water but not more pressure then parallel is best?hot_rod said:
24 gpm would be a lot to shove thru a 1" pipe. But if you are getting the sprinkler coverage you need with the series pumps, that is the win.
Just a guy running some pipes.0 -
Changing one thing affects everything else. If the pipe size and heads are causing restriction then series will overcome the added head (hopefully). Two pumps in parallel with the same head will only pump tp that head.
Put a flowmeter and some gauges on it to approximate the head0 -
Think of it like a hydronic system. If you knew or could calculate the pipe length, fittings, heads, etc you could come up with a head number. Say if you want 20 gpm at that head, look to the pump curve.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements