Hi all. I have a Lochinvar Noble NKC199. New construction house built at the end of 2018. I’ve noticed the condensation neutralizer capsule has slowly gotten dirtier (browner) as time has gone on, but has gotten significantly grimier over the last couple months. The capsule was full of a pellet-like substance and a liquid. Over the last couple months most of that liquid is gone, and what little left is a deep brown. Picture attached. Is this something that is normally cleaned during annual servicing? Is this something to be concerned about?
In case anyone was wondering if we actually got an annual service accomplished - the short answer is...partially, but mostly no. It’s a long story, but we were ultimately told that it “shouldn’t” need additional servicing this year. I’m not sure I believe the technician but I’d like to avoid a $ service charge this year if I can. Thank you.
In case anyone was wondering if we actually got an annual service accomplished - the short answer is...partially, but mostly no. It’s a long story, but we were ultimately told that it “shouldn’t” need additional servicing this year. I’m not sure I believe the technician but I’d like to avoid a $ service charge this year if I can. Thank you.
0
Comments
-
Anyone know anything about this?0
-
Until the pellets are about gone, or a brown sludge, you should be fine. I suppose you could open it up and flush the gunk out.
The liquid is only present if the boiler is condensing, so if it is just running high temperature for DHW production, you may not see much liquid.
Assuming there is no crack causing the liquid to leak.
Download the installation manual to be sure it is installed properly.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Just buy a new bag of them and change them...
https://www.suppliesdepot.com/buy/product/JJM-NBT-23R-ACID-CONDENSATE-NEUTRALIZER-REFILL-PELLETS/1121078?ID=/Water-Heaters-Parts/Condensate-Neutralizers/dept-29O
Note that I have the old Viessmann neutrilizer, which Viessmann no longer supplies the pellets for. So I ordered the JJM ones...
Perry1 -
The neutralizer outlet on the left should be at the top, not the bottom. With the way you have it now, the condensate will run straight through, only reacting with the small amount of pellets at the bottom. The water may not even come out neutralized properly.With the outlet at the top, the neutralizer will amass condensate and allow all the pellets to be in contact.Should be an easy fix.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
-
Depends on which direction you are flowing?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements