Opinions on new piping scheme
dave123
Member Posts: 67
So after a lot of back and forth, I've sketched out a diagram of the piping for a proposed hot water heat system for my (older) home. Pic below. Three zones based on common heat loss rates, taking into consideration some of the physical limitations of the house. These would be new rads, with TRVs but also isolation valves to do a bit of balancing. These are all direct return; the only zone that could be (somewhat) easily piped home run would be zone one. Just the main floor rads are shown; zone 1 is above a heated basement, zone 2 above an unheated garage, zone 3 is partly above both. Just looking for some initial feedback. Thanks.
0
Comments
-
No it is all wrong
There was an error rendering this rich post.
0 -
What has made you decide on this two pipe system?0
-
You mean as opposed to all home run? All of zone 2 needs to be placed in or on the ceiling of the unheated garage, so home run would mean a lot of the ceiling of the 700 SF garage would need to come out and be replaced, or all run on the surface, where there's already lots of obstructions. Zone 1 could be home run, but the pipes of zone 3 are already pretty short.Intplm. said:What has made you decide on this two pipe system?
What piping arrangement would be preferable?0 -
A reverse return would be a bit more "self balancing"
A delta p circulator with the TRV would help assure correct flow as the valves modulate.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
dave123 said:
You mean as opposed to all home run? All of zone 2 needs to be placed in or on the ceiling of the unheated garage, so home run would mean a lot of the ceiling of the 700 SF garage would need to come out and be replaced, or all run on the surface, where there's already lots of obstructions. Zone 1 could be home run, but the pipes of zone 3 are already pretty short.Intplm. said:What has made you decide on this two pipe system?
What piping arrangement would be preferable?</blockquote
I was just wondering if you had considered a series loop system? Like this ? But with the circulator on the feed and not the return as shown......Pumping Away .0 -
What would be the advantage of a series loop (all one zone?) over the 3 zones with two-pipe?Intplm. said:dave123 said:
You mean as opposed to all home run? All of zone 2 needs to be placed in or on the ceiling of the unheated garage, so home run would mean a lot of the ceiling of the 700 SF garage would need to come out and be replaced, or all run on the surface, where there's already lots of obstructions. Zone 1 could be home run, but the pipes of zone 3 are already pretty short.Intplm. said:What has made you decide on this two pipe system?
What piping arrangement would be preferable?0 -
If you series loop heat emitters each downstream emitter sees a lower supply temperature, that would need to be calculated to assure adequate heat in each room. With panel rads, 3 maybe 4 per loop depending on the radiator size, ∆T you are designing around. There is some math in here to help with lower SWT adjusting.
https://www.caleffi.com/sites/default/files/file/idronics_25_na.pdf
You have a few choices for piping as you know. Diverter tee, home run, series, parallel as well as various return piping options.
It comes down to what you or an installer finds to be the best method for the application.
It could be based on ease of installation, structural restrictions, zoning options, cost, type of radiators, installers skill, multiple temperature zones, etc. All have pros and cons, some are better for specific applications.
Looks like you have a blend of parallel and series going on.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I think the only segment that is series is the short pipe between the two baseboard units, which will run through the wall between the two bathrooms. The rest should be parallel direct return.
Was just looking to see if anyone could see any obvious oversights. If there's flow meters on the zone returns at the boiler, then the only potential problem I see would be the more distant rads being short-changed on flow, if the TRVs don't cut it in really cold weather. And that could be fixed by adding a few balancing valves, correct?
I could change zone 1 to a remote manifold though, and home run from there.0 -
If you go with TRVat ever radiator and a delta P circ, it should work fine. TRVs work regardless of cold weather:) They are responding to the temperature at the TRV, not outside, as is the radiator.
With fixed speed circulators on multi zoned, multi emitters balance valves are used to fine tune, assuring best heat distribution and most efficient operation. It may be a bit over-kill for a small residential project. No harm is adding valves to the various zones for checking and confirming flow rates, like a 132 Quicksetter.
TRVs and variable speed ∆P circulator, ODR boiler control should get you a very nice system, possibly constant circulation once dialed in properly.
To me an ideal system would be a boiler and distribution that continually modulates to ever-changing loads. Modulating boilers, TRVs and ∆P circulators can get you very close to that operating condition.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
But the system as diagrammed, especially zone 1, runs the risk of the early rads taking too much flow and leaving the last ones with too little flow, doesn't it? On the coldest days, presuming the TRVs on the early rads are wide open, that's going to rob the end rads of enough flow, no?0
-
My recommendation would be a home run distribution system using 1/2" Pex-Al-Pex, manifolds with flow balancing capabilities, Delta P pump, TRVs.Steve Minnich0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements