Mitsubishi Mini-split Branch Box question
Stoli
Member Posts: 10
Residential 5 port Mitsubishi branch box: PAC-MKA51BC
If only 4 of the 5 ports are used, does it matter which ones? The install manual sort of insinuates that you should use A, B, C and D and leave E unused, although it sounds more like a recommendation than a requirement. My installer used A, B, D and E and left C unused, presumably because port E has a 1/2" gas line (the other 4 are 3/8") and one of the inside units was larger and required a 1/2" line. That way, he didn't need to install a 3/8" to 1/2" converter pipe.
If only 4 of the 5 ports are used, does it matter which ones? The install manual sort of insinuates that you should use A, B, C and D and leave E unused, although it sounds more like a recommendation than a requirement. My installer used A, B, D and E and left C unused, presumably because port E has a 1/2" gas line (the other 4 are 3/8") and one of the inside units was larger and required a 1/2" line. That way, he didn't need to install a 3/8" to 1/2" converter pipe.
0
Comments
-
Does not matter which ports you use. Does not have to be sequential, at all. But, you have to select the correct addressing for the wiring. Every time I do a D box, too many months have passed and I can’t remember the exact process. It’s buried in my notes somewhere0
-
Cheers Gary. I appreciate you taking the time to respond.0
-
Thought its 15 and 51 (condenser first then box)0
-
Probably important to note that there may be differences depending on the models, but in my case, I have a newer MXZ condenser and the PAC-MKA51BC branch box with 4 indoor units hooked up, so the addressing setup is:
Condenser: 51 (SWU2, SWU1)
Branch Box:
Address: 01 (SW12, SW11)
SW1: Active ports (A, B, D, E) set to ON
That effectively addresses the indoor units to
A : 01
B : 02
C : (NOT USED)
D : 03
E : 04
Gets a little more complicated with multiple D boxes, but the manuals are pretty good regarding proper addressing setup.
** NOTE: I'm not a Mitsubish Tech. **
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements