Weil Mclain Ultra indirect domestic hot water fault
Options
Hort
Member Posts: 5
Recently I have noticed that during most calls for domestic indirect hot water heating that the return temperature is a few degrees hotter than the supply temperature and I get a lockout that automatically resets itself in time.
I have a post pump time set for 20 sec. but there does not seem to be a pre-pump time to set that may keep this from happening. This is DHW priority 1.
This is a recently new situation but has occurred during the heating season and now during warm weather shut down for house heat. Weil Mclain Ultra 105 series 3
Any thoughts?
I have a post pump time set for 20 sec. but there does not seem to be a pre-pump time to set that may keep this from happening. This is DHW priority 1.
This is a recently new situation but has occurred during the heating season and now during warm weather shut down for house heat. Weil Mclain Ultra 105 series 3
Any thoughts?
0
Comments
-
Max supply 160.
mod on diff 2
mod off diff 10
Max rate 94%
Min rate 20%
Lockout usually occurs during first call for hot water in early morning0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 431 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements