Connecting Entran 3 to Pex-Al-Pex
https://www.supplyhouse.com/Bluefin-PXF050-1-2-PEX-x-1-2-NPT-Brass-Female-Adapter-Lead-Free
to:
1/2" Male threads to 1/2" pex press as seen here:
https://www.supplyhouse.com/Viega-90521-Zero-Lead-Bronze-1-2-PEX-Press-x-1-2-M-NPT-Adapter-w-Attached-Sleeve
The Entran 3 was here when we moved in so I have never made a connection with it or ever used it. Am I thinking right? Will this approach work to connect the two hose?
Comments
-
-
-
@kcopp The tubing doesn't feel too bad. @SuperTech
Unfortunately, I cannot replace the Entran 3, because it is in the cement slab, the rest of the house will be pex-al-pex, but the basement runs are permanent. The reason I need to connect to the Entran 3 is because I am installing a new manifold and where I want to put it would require some longer tubing off the basement Entran 3 coming out of the floor.0 -
You are fortunate.
The in slab set up probably helps w/ the O2 ingress.
That and that slab set up require lower water temps.0 -
What size Entran? Look like some suppliers still have the sweat to barb adapters, sweat into the Appropiate Pex al Pex fitting. Also you the Watts selftite clampshttps://www.supplyhouse.com/Onix-Fittings-12870000Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The Entran is 1/2". Thanks guys.0
-
I would definitely use the Watts barb Onix adapters, not a universal hose barb connection. Not sure if they offer threaded adapters, you may end up sweating together adapters.
Here is an example with a couple pex barb choices. This is a 3/8 Onix barb to 1/2 PexBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@hot_rod Thanks. I actually took an old Entran 3 coupling out of the hose and took it to the hardware store. It actually was a 3/8" barb. The barb is the same as a garden hose barb so I bought those, but now I am a little scared based on your comment. I purchased 3/8" barb to 1/2" female thread so I am going to try that and see how it goes.0
-
Give it a try, at low pressure you may be fineBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Entran lost a class action suit and a compensation settlement fund was provided. I don't know the status of that now.
I never used it because I replaced a lot of car radiator hoses and I was wise to what happens to rubber and hot water, nor did I ever use that Shell gray crap either. If I had saddled a customer with that stuff, I would feel bad it today.0 -
@HomerJSmith I did look into the Entran lawsuit. It was specifically related to Entran 2, so hopefully Entran 3 will hold up better. If I could redo it, I would, but unfortunately, with it being in the slab, just have to work with what I got. @hot_rod I do appear to have a clogged line though, any info on how to release the clog?0
-
The bigger issue with rubber tube, then and still now, seems to be O2 ingress somehow that causes ferrous metal breakdown and sludge formation. Sometimes you can flush it by applying your building water pressure, maybe 60 psi or more.
Most pros have a flush cart, high pressure high gpm that they use to clean those systems. With 10 gpm or more you can flush multiple loops at a time to speed the process.
Flush into a white bucket or barrel to see when you have it flowing clear.
Once loops are all open, add and circulate a hydronic cleaner to free up and wash out all the remaining sludge.
Once you have it all flowing, put in good quality, low TDS water and add a conditioner like Fernox or Rhomar. Those hydronic conditioners have O2 scavengers. It will need an inhibitor boost from time to time. Keep temperatures as low as possible to slow O2 ingress.
Even the newest version of that rubber tube seems to be prone to sludge, this was sent to me recently, after a few years of service.
After you flush see if a magnet attracts the sludge, proof that it is metal breakdown, not the clay dissolving from the tubeBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I have used a 1 hp submersible well pump in a 55 gal drum of water to try and "free up" some radiant loops of this kind of tubing installed in slab in the 1980s. It was this same red-brown sludge. Two loops I couldn't get flow through and had to abandon them. I think I was the first to ever flush them.0
-
Hi hot_rod,hot_rod said:I would definitely use the Watts barb Onix adapters, not a universal hose barb connection. Not sure if they offer threaded adapters, you may end up sweating together adapters.
Here is an example with a couple pex barb choices. This is a 3/8 Onix barb to 1/2 Pex
I know this has been awhile, but I am working on it now. In the adapter photo you provided above of the barb one side and pex the other, where did you find that? I am looking for a 3/8" barb to 1/2" pex and I am struggling to find it.0 -
I made my own, looks like SupplyHouse has the adapters.
Also use the spring type clamp, not a stainless screw type. The spring clamps keep a constant tension better.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Awesome thank you. I actually tried a 3/8" pex to 1/2" pex adapter and use the screw clamps on the Entran side and the cinch rings on the pex side. It sort of worked. Some of the Entran tubes have ridiculously slow drips, so close, but no cigar, hence me asking about the adapter.hot_rod said:I made my own, looks like SupplyHouse has the adapters.
Also use the spring type clamp, not a stainless screw type. The spring clamps keep a constant tension better.
Just for the sake of experiment, I am going to try a cinch clamp on the Entran side just to see what happens. 1/2" rings were too small, but the 3/4" were too big, so I ordered some 5/8" from Supply House, we will see what happens.
Anyway, I appreciate the help.0 -
It really needs to be the Onix adapter, it has a taper built in, unlike a hardware store adapter. Also the clamp needs to be able to "self tighten". At one point a rubber cement was used with the barb.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Mcmaster-carr might be a good lace to look for odball size hose barb and spring clamps.0
-
Yeah, it seems like that is what will end up happening, but since I have everything torn apart anyways, I thought I might as well experimenthot_rod said:It really needs to be the Onix adapter, it has a taper built in, unlike a hardware store adapter. Also the clamp needs to be able to "self tighten". At one point a rubber cement was used with the barb.
0 -
Is there a layer of aluminum in that tubing?0
-
I'd be inclined to buy the correct clamps, designed and engineered to work with that tube and barb.
Both 1/2 & 3/8 are at SupplyHouse.
E3, then E3∆, orange colored, then the black colored Onix, which has the aluminum layer.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Oh. i asked the question, then i read the title and thought oh, wait it is right in the title. But then i thought if there is a layer of aluminum, how is oxygen getting in.Prevch said:0 -
So just to update everyone, I was able to get the project completed successfully. The sandy junk that was stuck in the Entran lines I was able to successfully flush with the house water pressure. To connect the Entran 3 to the 1/2" pex-al-pex, I used 3/8" pex to 1/2" pex adapters. On the pex side, I used 1/2" cinch rings, on the Entran side, used hose clamps. A few of the hoses did have a very slow leak, but adjusting the clamp seemed to fix that. It also helped when heat was run through it from the expansion. Seems pretty solid right now, don't know how long it will hold up, but I am going to keep my eye on it. Attached are some pics. Thanks so much for everyone's advice and help.
0 -
Not ideal, might work for awhile.
That type of hose clamps will eventually cut through the jacket and O2 barrier. And may need occasional tightening as that hose expands and contracts from hot to cold, that is why the constant tension clamps are used. The more you chinch that hose clamps the more they damage the tube
You should not need to distort the Onix tube like that to get a tight seal.
The Onix barb is a fairly specific fitting, took about 6 years to get it right. The correct combination of barb and clamp will not leak from day one, or sunset day. A pex barb is far from a hose barb as you can see just looking at them.
Other than that...:)Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I hear ya, I am sure I will have to change it again in the future, but I was being stubborn lolhot_rod said:Not ideal, might work for awhile.
That type of hose clamps will eventually cut through the jacket and O2 barrier. And may need occasional tightening as that hose expands and contracts from hot to cold, that is why the constant tension clamps are used. The more you chinch that hose clamps the more they damage the tube
You should not need to distort the Onix tube like that to get a tight seal.
The Onix barb is a fairly specific fitting, took about 6 years to get it right. The correct combination of barb and clamp will not leak from day one, or sunset day. A pex barb is far from a hose barb as you can see just looking at them.
Other than that...:)
I have spent so much money on this project, three cross manifolds, tons of pex, press tool and press fittings, etc., I REALLY didn't want to buy more fittings, but it will probably come back to bite me. Stay tuned!0 -
Norma is a brand of gear clamps that are smooth on the inside, a better clamp for soft rubber.
Or this bolt and nut type common at auto part stores. This type was actually the very first Heatway clamp, until they discovered the need for constant tension type.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thank you!hot_rod said:Norma is a brand of gear clamps that are smooth on the inside, a better clamp for soft rubber.
Or this bolt and nut type common at auto part stores. This type was actually the very first Heatway clamp, until they discovered the need for constant tension type.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements