L8124C operating logic
What I don't understand is if the hi limit will turn the boiler on and off as needed what is the purpose of the low limit settings. Is it to allow for a larger heating range when calling for domestic hot water?
So was I right to assume that the analog Press/Temp gauge should correlate with the temp settings of the L8124C
Comments
-
The dials aren’t very accurate, especially over time. Best to go with a digital one like the Hydrostat 3250 plus.
170/210 is way too high.
If you need 170 lo to make enough domestic hot water, or 210 to keep your house heated, you have other issues that should be addressed.
https://usermanual.wiki/Honeywell/HoneywellAquastatL8124CUsersManual261448.1027255968-User-Guide-Page-7.png
There was an error rendering this rich post.
0 -
Most typical systems I deal with work well with a setting of 140/180. The 140 temperature is to keep the boiler from dropping down to the point where it will condense.
Basically, with a no heat call, the boiler will drop down 10 degrees below the low limit setting, if the differential is 10 degrees, and shut off at the differential setting.
On a call for heat, the boiler will run until it reaches the high limit setting, and then come back on when it drops down 10 degrees. This is a fixed differential.
Rick0 -
thanks, very helpful!0
-
I know this is way late but, in case anyone is searching for info on this subject, I’ve posted an image of my heating system here with the associated controls. Important to note is that the high limit control setpoint has its own built in -10 (delta) degree setting. I.E., if you set it for 180 it triggers at 170. Additionally, the differential setting must be AT LEAST 20 degrees between the high point and low point physical settings. My diagram supports my bi-level home in the northeast, with typical teen to 100 temperature ranges.
Without further adieu…
I hope this helps!
Interpret how I say it, not how you think it.0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements