Air blocking steam and gauge glass stability.
ChrisJ
Member Posts: 16,315
@Hap_Hazzard
Here's a single video showing the behaviors I mentioned in other threads. No pigtail on those gauges and the Magnehelic has the inlet connected to the front of the gauge, the face and lens is literally pressureized. If steam ever got to it you'd see condensation immediately. Not to mention it would probably destroy it. It's been on there for 5+ years now and it's never off. This set of controls is used to control the Ecosteam as well as for me to observe what's going on. It's not the primary set of safeties.
My boiler also has a proper pig tail on it's code required 30 PSI gauge and Pressuretrol. This isn't optional.
Also, no water dumping over the top of the gauge glass, seen near the end of the video.
I'm really not sure why you believe water dumping over the top of the gauge glass is normal but it isn't. It usually means you need to do a lot of skimming or reduce water treatment.
https://youtu.be/hH36luC9GKU
Here's a single video showing the behaviors I mentioned in other threads. No pigtail on those gauges and the Magnehelic has the inlet connected to the front of the gauge, the face and lens is literally pressureized. If steam ever got to it you'd see condensation immediately. Not to mention it would probably destroy it. It's been on there for 5+ years now and it's never off. This set of controls is used to control the Ecosteam as well as for me to observe what's going on. It's not the primary set of safeties.
My boiler also has a proper pig tail on it's code required 30 PSI gauge and Pressuretrol. This isn't optional.
Also, no water dumping over the top of the gauge glass, seen near the end of the video.
I'm really not sure why you believe water dumping over the top of the gauge glass is normal but it isn't. It usually means you need to do a lot of skimming or reduce water treatment.
https://youtu.be/hH36luC9GKU
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Comments
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements