Grundfos UPZCP-3, 3-Zone Pump Control - Set-up?
Hydronicolic
Member Posts: 16
I have a 2-zone RFH system being heated with a Tankless Heater. I have the 3-Zone Pump control set-up with the Tankless pump on the 3rd zone relay. I wired the End-switch terminal over to the TT terminal on the 3rd relay thinking, on a call for heat, the end-switch will make and start the Tankless pump. When ALL calls are satisfied, the End-switch opens and the Tankless pump shuts off. What is happening: it works on the start-up, but when ALL zones are satisfied, the End-switch doesn't open unless I kill power to the Control, leaving the Tankless pump running continuously. THE QUESTION: Is there a way to make this work?
0
Comments
-
A single pump system? Does the tankless supply DHW also? Or just dedicated to heat?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Dedicated.0
-
I've used a separate single zone relay in the past but thought, "what the heck" save the cost and labor of the 2nd control.
I was wondering if tying in a resistor between the E.S. and the 3rd Zone relay TT might create enough load to make this go away, while realizing I'm not an electrical engineer.0 -
If you are trying to control 3 circulators a ZVR?
\The ZSR is the control for switching circulators Zone Switching Relay
The ZVR Zone Valve Relay is a 24V relay for powering zone valves.
There may be a work around
You have 2 zone pumps and a boiler primary circ that needs to run with either zone circ?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
That is correct. 2 Zone pumps, and 1 Heater pump on the 3rd Zone relay contacts.0 -
Wire your primary pump to the "Primary Pump" terminals with all the dip switches in the off position. Remove the wires from the end switch to zone 3 TT terminals.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I see a problem with the vent pipe connection to the Takagi boiler. The installation manual says the vent pipe must be inserted inside the collar, not outside. This is to ensure that a leak-free seal can be made with the o-ring inside the collar.
Here's what my last Takagi install looks like.
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements