Weil-Mclain V68 boiler
Options

Saintrojo
Member Posts: 1
Intermittently my boiler trips out and I need to bleed it 2 or 3 times to get her running again. New aquastat in 2016, new flame sensor in 2017 and a new transformer in 2019.
0
Comments
-
V68 Boiler is an oil fired boiler that is over 25 years old. Annual maintenance is a must for that boiler. A new Aquastat is not a complete maintenance.
This sounds like you may have a fuel line leak that is letting air into the sealed fuel lines. you will need a vacuum gauge and a few oil line fittings to check the piping from the tank to the burner. This is assuming that you get air from the bleed port each time you "Bleed it 2 to 3 times".
look at this from beckett https://www.beckettcorp.com/support/tech-bulletins/successfully-locating-suction-line-leaks/
testing fuel lines was addressed several times on this site here is one of them https://www.beckettcorp.com/support/tech-bulletins/successfully-locating-suction-line-leaks/
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 989 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements