Age of a Crane 20 Boiler # 20-B Series X-A
NarrowGateFarm
Member Posts: 1
in Oil Heating
I'd say probably 1940s or early 1950s. The burner is newer and, depending on what head is on it, might be a decent one. I ran into a similar one here, that someone had made a mess of:
https://forum.heatinghelp.com/discussion/170456/door-mount-disaster-or-ohhhhh-this-is-just-wrong
Where are you located?Baltimore, MD, USA
Consulting0 -
Dirt...old as dirt. At least you can stick your entire head in there and look at the flame.
You're barometric dampers are installed incorrectly on both appliances. Ok that way for gas, not for oil.
2 pipe oil... @EBEBRATT-Ed will be so happy
@STEVEusaPA ,
This made my day. I spotted the two pipe right off the bat but you beat me to the punch
2 -
Btw, does anyone know what this means in the nameplate?
“Valve Capacity 292 lbs/hr”There was an error rendering this rich post.
@STEVEusaPA
Oil firing rate is 2.00gph so 2 x 140000=input of 280000
Safety valve capacity of 292lb/hour is 292 X (btus in a lb of steam which is 1000) so 292 x 1000=292,000.
There just telling you what the minimum size safety valve should be.
2 -
Thanks @EBEBRATT-Ed. So, is that for the PRV? If so, what's the conversion? Just wondering...
It is for the relief valve. If you look closely on a relief valve they have a rating of how much energy they can dump when they open.0
Was this at a time before they just universally decided for residential-30 psi for water & 15 psi for steam?
@STEVEusaPA
Pressure isn't an issue steam is 15 psi. It's just another way of expressing the BTUs that the steam relief valve must pass.
For some reason on smaller boilers they usually use BTU/HR.
But on old residential (like above) and larger commercial stuff they use LBS of steam/ hour for the valve capacity.
On low pressure (under 15psi) the BTUs/LB of steam is usually considered to be 1000 btu/LB.
I think it's actually 970/LB at 212 degrees. But the btus/LB varies with the steam pressure1 -
@NarrowGateFarm , where are you located?
Consulting0