New cast iron boiler
Snowmelt
Member Posts: 1,428
Would you or is it a good option to use a cleaner and an inhibitor on a cast iron boiler?
Whir I said that would you also use a magnet in line?
Whir I said that would you also use a magnet in line?
0
Comments
-
I use a dirtmag on my cast iron boiler, gotta protect the ECM Pumps.0
-
does anyone do primary / secondary on cast iron boilers ?0
-
-
nice I want to see a pic,
0 -
You can primary secondary pipe a cast iron boiler. Make sure return water temp is 140 F so the cast iron boiler does not condense.
You can put a dirt magnet 🧲 on any boiler.
Check with the boiler manufacturer to see what type of cleaner and inhibitor you can use in their cast iron boiler.
Fernox claims when you clean a old boiler system with their cleaner you can transfer the heat from the water to the cast iron radiators, cast iron baseboard or copper baseboard faster saving up to 15%.
So putting a new cast iron oil or gas boiler or condensing gas boiler into a old heating system and not flushing and cleaning out the system you are not doing the best you can do for your customer.
Sure everyone looks at the boiler AFUE but that is only one part of a Hydronic heating system. You need to look at the complete system.
New boiler plus flushing and cleaning the system and then running the boiler and heating system at the lowest supply water temp you can to heat the house you can really save your customer some good money on their heating costs.
1 -
@Snowmelt
I would primary/secondary any boiler. It's the only way in my opinion that you can be 100% sure that you have the right flow through the boiler at all times no matter what the zones are doing2
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements