Radiator vents open and close repeatedly
jimb245
Member Posts: 6
Lately my radiator vents are opening and closing repeatedly, especially during the initial part of a cycle. The open and close times are around a minute or so. The vents hiss fairly loudly when open and make a noticeable sound when they close. The vents were replaced a few months ago. The radiators are single-pipe. Anyone know what could cause this and whether it means something is amiss?
0
Comments
-
What make of radiator, and main vents are on the system?
What is the pressure of the system?—NBC0 -
Your steam pressure may be set to high.
Your boiler pressure should be no more than 3 PSIG with a 1 pound drop back.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
The embossing on the radiators is American Radiator. The main vents are Dole Valve No 3C - they probably havent been serviced for a long time. The pressure gauge on the boiler always reads zero so guess it's not functional. The cut-in pressure setting on the pressuretrol seems to be at the lowest point (picture attached) and the cut-out wheel shows a "1" when viewed from the opening of the box.0
-
I think a 3C is for convectors, like a Hoffman 71C. That's pretty small for a main vent.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thanks. Guess I need to get the vents and pressure checked.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements