Prestige Solo PS110, E18 error code

I've been servicing this boiler for a few years now. Lately, it's been locking out with an E18 error code: "exceeding 212°F". I checked the outlet sensor by confirming the screen temperature with actual water temperature. The onboard circulator seems to be working properly and the house heats properly when the boiler is working. I'm never there when the error message pops up.

Curiously, the original contractor installed used a Grundfos Alpha ECM pump for DHW. It was on AutoAdapt and I switched it to constant speed and they are still getting the error message.

The factory says to change out the Alpha, that they can be troublesome for DHW. Haven't done it yet, but I'm wondering if anyone else has had the same problem.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • DZoro
    DZoro Member Posts: 1,048
    Have not seen that one. I'm assuming you have a separate domestic tank? How is the domestic pump being controlled? From the boiler or a pump controller? Is this the first generation TT?
    D
  • DHW pump is being controlled from the boiler. I think it's a second generation TT.

    It's been running fine for years before this cropped up. I want to check the post-purge run time for the pump when I go back. Also, the DHW temperature limit.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab