Burnham gas steam furnace pilot light goes out every 3 to 4 hours

replaced thermocouple, pilot orfice, gas valve, new gas line from pilot to gas valve
thermocouple is installed correctly and has a strong blue pilot flame
pilot light goes out if its a windy day or not, and there is no obstruction in venting
this has been an ongoing problem for a month, pilot will light and furnace will produce steam
but shuts down after few hours, pilot can be relit right after it shuts down and the cycle continues
any ideas???

Comments

  • HVACNUT
    HVACNUT Member Posts: 6,338
    Any changes made or added? Range hood, new dryer, newly enclosed equipment room, etc.
    Is there adequate combustion air?
  • helpme123
    helpme123 Member Posts: 3
    no changes whatsoever and adequate combustion air, no draft either to blow pilot out,
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    Have you a chimney liner? Is there any water or steam condensing and dripping on the pilot? Have you thought of an electronic ignition upgrade? The lowest cost is a pilot re-light. available from White-Rodgers 5059-23 or Robertshaw 785-001. but there are more with different kits with different accessories

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?