Burnham gas steam furnace pilot light goes out every 3 to 4 hours

replaced thermocouple, pilot orfice, gas valve, new gas line from pilot to gas valve
thermocouple is installed correctly and has a strong blue pilot flame
pilot light goes out if its a windy day or not, and there is no obstruction in venting
this has been an ongoing problem for a month, pilot will light and furnace will produce steam
but shuts down after few hours, pilot can be relit right after it shuts down and the cycle continues
any ideas???

Comments

  • HVACNUT
    HVACNUT Member Posts: 5,803
    Any changes made or added? Range hood, new dryer, newly enclosed equipment room, etc.
    Is there adequate combustion air?
  • helpme123
    helpme123 Member Posts: 3
    no changes whatsoever and adequate combustion air, no draft either to blow pilot out,
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,713
    Have you a chimney liner? Is there any water or steam condensing and dripping on the pilot? Have you thought of an electronic ignition upgrade? The lowest cost is a pilot re-light. available from White-Rodgers 5059-23 or Robertshaw 785-001. but there are more with different kits with different accessories
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics