Navien NCB-180E

JCPHNY
Member Posts: 1
Why does Navien forbid connecting 120 power to external circulator ? Draw on taco pump is .7 amps. Navien external power is 1.3 amps !
0
Comments
-
Inrush coil trip the internal breaker then you have no heat or dhw.
That being said I recall us wiring up a small 3 speed pump running on low speed.
But best to spend the $50 on a switching relay And do it right to avoid issues.0