Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Navien NCB-180E
JCPHNY
Member Posts: 1
Why does Navien forbid connecting 120 power to external circulator ? Draw on taco pump is .7 amps. Navien external power is 1.3 amps !
0
Comments
-
Inrush coil trip the internal breaker then you have no heat or dhw.
That being said I recall us wiring up a small 3 speed pump running on low speed.
But best to spend the $50 on a switching relay And do it right to avoid issues.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements