oil heater

cutterjoseph
Member Posts: 2
in Oil Heating
I changed out my old transformer and control for the newer Becket electronic pieces, the old pump had no solenoid, the new pump has one. Will it work with a 7505a controller? Should all the wiring be done as directed in the diagram? Wii the solenoid delay the oil starting to flow and stop the puffing?
0
Comments
-
The A doesn't have pre and post purge. It's basically a 3 wire control. You can wire the solenoid with the burner motor and it will open and cut-off, but no pre/post purge. You would either need a universal Genysis (I think a P) and the contractor tool to program it.
Or stick a Carlin ProMaxx, or Honeywell R7248U in and program it yourself.steve1 -
-
Thank you for the info, what do you think could be causing to go PUFF? Every time it starts.0