Best way to pipe 2 Hydronic coils same zone
Ray B.
Member Posts: 3
Looking for best way to pipe in 2 hydro coils in existing duct work, same hydronic zone as not to overfeed 1 coil & vs other. Was thinking just putting in full port ball valves on return of each coil for balancing? 1 coil is 10x10 & other is 22x12. Thanks for the help!
A dedicated circulator for the two? Do you know the required flow rate?
This is a user friendly "setter" it allows you to set, confirm, and check flow rate.
https://www.caleffi.com/sites/default/files/file/01149_20_na.pdfBob "hot rod" Rohr
Living the hydronic dream1 -
Hot Rod Yes dedicated circulator for the 2 coils. 1 coil is 2.5 & other coil is 5 GPM (just coil) . approx 25-30' of piping (1 way). Total Btus approx 95,000 (1 coil is 24.7 k Btu & other is 70k)
1" pipe I'M assuming? Thanks in advance0 -
A wide array of balance valves available, depending on the accuracy you want and the $$ you want to spend.
Ball style like the B&G Circuit Setter or Caleffi 132 quicksetter are perhaps the most common.
Or a fixed orifice type, variable orifice style, PIB pressure indépendant.
The Quicksetter may be the only style with the gpm readout built in. Most others would require a ∆P gauge connected to the test ports to dial in and exact flow rate.