rinnai RL75i code 10

Our Rinnai RL75i water heater has been giving us a code 10 after 8 years of flawless operation. I have flushed the heat exchanger, cleaned the fan and cleaned the burner with the help of an excellent Rinnai service tech. The exhaust and air intake are clean and unobstructed. The tech thoroughly checked the unit and said everything looked ok. We are still getting the code 10, usually from running bath water in the upstairs bathroom. If we turn off the water and turn it back on everything is fine although occasionally we have to do this a second time and rarely a third time. The tech said if the code 10 continues the next step would be a more complicated check of the electronics. Can anyone give me any ideas on what to do next?

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,380
    edited December 2019
    Code 10 is a "blocked vent" code. The indications are that your air intake or exhaust may have some restriction. This is measured by an air pressure sensor. You may have a blocked vent, remove the blockage. You may have a build up of dirt on the fan that provides combustion air, Clean the fan. you may have a defective sensor, replace the sensor

    The code indicates the approximate cause of the fault, and gives a direction to start looking. Most problems with Tankless water heaters are low gas pressure or blockage in the water side of the heat exchanger due to build up of minerals. Code 10 does not point in that direction. Look at the path the air for combustion takes to get in, and the path the byproducts of combustion takes to get out.

    There are 2 sides to the heat exchanger, the fire side and the water side. Looks like you have been diligent with the water side. Have you checked the fire side where the hot exhaust gasses go to transfer the heat to the water?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • srhfb
    srhfb Member Posts: 3
    Thanks for your reply. We have removed and cleaned the burner. This was done with the assistance of a certified rinnai service tech. I would assume he checked the exhaust when we removed and cleaned the burner.
  • srhfb
    srhfb Member Posts: 3
    What sensor do you mean and where is it located?
  • conserve
    conserve Member Posts: 1

    I have a Rinnai CU160i indoor tankless heater and for the first few months after installation, it ran fine. Then, occasionally, I would get Code 10 and no hot water. My outside air intake (6 ft run of PVC pipe with 6 elbows) and exhaust vent lines were clear, so it had me puzzled. I eventually replaced the fan. The unit then ran fine for a few months, but then the dreaded Code 10 came up again, on occasion. After some thought, I cut the air supply line from outside and let the unit draw air from inside with just a short piece of PVC, a few inches long, and an elbow. Since then, no Code 10! In my (humble) opinion the 6 ft long length of pipe to draw air from outside caused too much air-flow friction and the fan couldn’t pull sufficient air. The Rinnai Install Manual allow installing with a pipe to draw outside air, or the double-wall pipe. My advice….just use a short pipe of pipe for the air intake from inside the house, and don’t try to pull from outside. A simple fix if it's your setup!

  • psb75
    psb75 Member Posts: 906

    I'm going to surmise that "6 elbows" are also kind of a "drag."