radiator not hot after circulator replacement
steamedchicago
Member Posts: 72
I have a Peerless cast iron boiler, feeding what was once a gravity system. Single zone, circulator pumping into the boiler. There was a Bell and Gosset NRF-22, which failed a week ago. I replaced it with a Grondfos UPS15-58. Now, I have a basement radiator that won't get hot.
My near boiler piping is a bit of mess. Coming out of the boiler, the supply Y's off into two 1 1/4 trunks, one serving the front of the house, the other the back. Coming off the branch for the front, there's a tee splitting off a 3/4 line that feeds the not hot radiator. The return for that radiator is hooked into the return for the radiator on the first floor directly above it. The 3/4 supply pipe is not hot past a foot or two from the split.
I assume the problem is that the B&G moved a bit more water, and could get flow into the small pipe. I have the grondfos on high. Is the best alternative to cut into the pipe, and put another circulator to drive water to our cold radiator?
My near boiler piping is a bit of mess. Coming out of the boiler, the supply Y's off into two 1 1/4 trunks, one serving the front of the house, the other the back. Coming off the branch for the front, there's a tee splitting off a 3/4 line that feeds the not hot radiator. The return for that radiator is hooked into the return for the radiator on the first floor directly above it. The 3/4 supply pipe is not hot past a foot or two from the split.
I assume the problem is that the B&G moved a bit more water, and could get flow into the small pipe. I have the grondfos on high. Is the best alternative to cut into the pipe, and put another circulator to drive water to our cold radiator?
0
Comments
-
Can you bleed the air out of that radiator/ line.
D0 -
There's no air. I get cold water as soon as open the bleeder on the radiator, and at the bleed fitting at the tee.DZoro said:Can you bleed the air out of that radiator/ line.
D0 -
Pictures, please. The Grundfos circulator on speed 3 is a good replacement for the Bell & Gosset.
Something else is going on. If it was working before and not now, I would suspect trapped air somewhere in that circuit.0 -
So, I closed the isolation valve on the return from the radiator (which I know was wet, because the stem leaks when its anything but full open or closed) and hooked a hose up to the boiler drain on the radiator (it's the lowest point in the piping, even lower than the boiler). I drained about five gallons of the nastiest looking and smelling water, which sounded like it had a bunch of air in it. The radiator is now heating up. I'll have to check in the next boiler cycle, too, but I suspect that's solved the problem. The air must have been trapped in the vertical pipe between the radiator, and the supply on the ceiling.HomerJSmith said:Pictures, please. The Grundfos circulator on speed 3 is a good replacement for the Bell & Gosset.
Something else is going on. If it was working before and not now, I would suspect trapped air somewhere in that circuit.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements