Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Air vent needed here?
CBRob
Member Posts: 283
I'm used to seeing an air vent here.
Is one needed if there is another air eliminater in the loop?
What is the typical size for an eliminater located here?
I also am used to seeing them on top of the indirect water heater.
Is that typically a 1/2 mpt?
Is one needed if there is another air eliminater in the loop?
What is the typical size for an eliminater located here?
I also am used to seeing them on top of the indirect water heater.
Is that typically a 1/2 mpt?
0
Comments
-
Yes that boiler comes with one specifically for that spot. It takes the air out of the H/E.
That one comes 1/2" for that tee.
D0 -
Thanks D0
-
What type of PVC is used for that exhaust?
Is it foam core PVC or Sch 40 PVC?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements