aquastat

I have a Honeywell Ra832A aquastat that will open up when I tap it. It will then circulate water for about a day until I tap it again. As you can tell by this post don't know much about this, any ideas.

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,269
    #1. This is not an aquastat.
    #2. The control is probably getting stuck intermittently or the electrical contacts on the relay are pitted and not making a good electrical connection. The percussion of tapping then moves the relay clapper or contacts to a position of better electrical contact to complete the circuit
    #3 They are inexpensive enough to just replace it
    #4 If you are not comfortable with electrical control wiring and the safe practices needed to properly replace the control, then call a professional plumber or heating contractor to do the work.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • HVACNUT
    HVACNUT Member Posts: 6,283
    The Taco SR501 is a good replacement for the RA832A. Pick one up, post back with some pics and we'll help you wire it if needed.
    Intplm.